hodaire

looking at a rewire for a block of 8 apartments, have a 3 phase supply in the basement, been asked to provide seperate metering next to the supply authorities meter.

be running an swa (not sure of size but possibly for 63amp single phase supply) to cu in each apartment

maybe also need to install a 3 phase board in the basement

can anyone suggest a fairly simple (easiest) way of providing this, are there any panel boards with meters already mounted etc...

apprieciate any help you can offer
 
Hi there and welcome to the forums.

I usually use the Merlin Gerin metering equipment myself, can be a bit more expensive though. Dorman Smith also do a good metering pack for their panel boards.

With the Merlin kit you can direct connect loads upto 63A, anything more and you would need CT metering

Can I ask why they require additional metering to the suppliers meter??

Cheers.

P.S link below.

http://www.schneider-electric.co.uk/electricity.nsf/results?open&query=meters
 
I maintain a few block flats for a housing association. There set up is as follows.

3 phase supply and meter from DNO is fed into a switch fuse then into a busbar chamber. From there tails are taken to a individual switch fuse for each flat and metered via a CT.

Simple but effective,

Ian
 

Reply to panel board / metering advice in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
811

Similar threads

  • Question
It sounds like the original meter was reading incorrectly and octopus aren't keen to admit this as they would probably have to refund you. I...
Replies
1
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top