Going slightly off piste on my D&V Project again.
I'm thinking of running parallel conductors for an electric gate supply 'just to learn about it'.

After reading the BGB it seems quite simple, in that the sum of two smaller cables will be the Iz of the circuit as long as the cables are roughly the same length, material, type, CSA and no branches or separate isolators!
Also, the In can be rated according to the current carrying capacity of both cables as long as they are protected against mechanical damage. Or, separate MCB's can be used for each conductor.


Is it really that simple?

The supply it's feeding is an electric gate, so I guess the thermal constraints could be worked out based on the gate only using power for 30 seconds(?) at a time so that a single cable would survive if the worst came to the worst.

Assuming you used twin and earth(!) for this. Would you run both Lines in one cable and the neutrals in the other, or not, or wouldn't it matter?

Many thanks.
Chris
 
Last edited:
It's not mentioned!
It might be saving money by using 2x 1.5mm2 as opposed to one 6mm2, although the cost of the extra MCB and mechanical protection might counter-act that :)

I mentioned I was using a 3-phase cooker the other day and nothing was said!
 
Last edited:
In your case, it may not be a cost effective alternative, to using a correctly sized single cable.

Generally, you would consider a parallel circuit on very long runs, or where there is a high current requirement or indeed in many cases, where both are involved.

One thing many electricians and engineers alike, often neglect to consider when deciding on installing parallel runs, especially when the larger cables are involved. That is the connections at both ends... This can be a real headache, and will often require ACB/MCCB terminal extensions, which is fine, ...if there is enough space for them, and the dressing of the cables!!!

So Yes it is very simple and straight forward, if everything is in your favour, but it can also get very involved, with other provisions needing to be made, in order for a parallel circuit to work!!!
 
Frankly, .... i don't know how he could of even asked that question!! I think he'd best stick to single cable installations for the time being!! lol!!!

I was wondering about induction. I'm still not too sure on how induction works, I need to read up on it. If you don't ask you never find out.
Also 523.7 BGB Part 1 a: 'the conductors in parallel are multicore cables'
Which, while eating dinner and rushing reading about parallel cables assumed it meant the same cable! :)
 
Thirdly if a cable was to get damaged I though it would be better if one with 2 Lines got cut through rather than a Line and Neutral which would leave a circuit with only half the current carrying capacity.
 
You mention 2 cables with an mcb for each one... so to isolate the circuit you need to switch off BOTH mcbs? Never heard anything like it!

You mention 2 T+E cables and then using both cores of one for Line and both cores of the other for Neutral???

No this sounds dodgy to say the least.
 
Thirdly if a cable was to get damaged I though it would be better if one with 2 Lines got cut through rather than a Line and Neutral which would leave a circuit with only half the current carrying capacity.

Stick to what you know!! ...Because it's quite evident, you don't know anywhere near enough about parallel supplies. ....i'm just hoping this is a virtual job your talking about, and not one in the real world...
 
Yes, it's for a D&V course.
I know very little about parallel conductors, only what I've read in about 10 minutes tonight. I though it might be something interesting to learn.

If anyone has a good link to anythng written about parallel conductors could you post it please!
 
Last edited:
You mention 2 cables with an mcb for each one... so to isolate the circuit you need to switch off BOTH mcbs? Never heard anything like it!

Reg (BGB) 434.4 Fault current protection of conductors in parallel
If operation of a single device may not be effective then one or more of the following measures shall be taken:
ii) For two conductors in parallel, a fault current protective device shall be provided at the supply end of each parallel conductor.

Is that refuring to something other than MCB's? Or have I interpreted it wrong? :)
 
Last edited:
Reg (BGB) 434.4 Fault current protection of conductors in parallel
If operation of a single device may not be effective then one or more of the following measures shall be taken:
ii) For two conductors in parallel, a fault current protective device shall be provided at the supply end of each parallel conductor.

Is that refuring to something other than MCB's? Or have I interpreted it wrong? :)

Imagine a ring circuit with only one point. Now that should resemble your parallel fed circuit.

There is only one overcurrent device protecting both cables isnt there.

Otherwise you could switch off one mcb, take the cable out and it would be live still as it's being fed from the other end!
 

Reply to Parallel Conductors. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
894

Similar threads

A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top