I have a ring circuit (circuit 1) and a light circuit (circuit2) in a flat im working on and i have somewhere in the walls or ceiling a joined earth path. From what i have seen there is no obvious metal conduit, so it seems its either the ventilation system that is fed by the same ring and goes to each room near the light circuit in question or one of the metal stud parts on internal walls.
I have tested between them and confirmed at light points and sockets that a path exists. I have added in a new shower circuit and extra sockets and some downlights. it was by chance i clipped the wrong earth when i had them out in the cu for the EIC that i discovered the shared earth path.
It is only between these two circuits, The flat is part of a newish building around 3 years old and is made mainly of a wooden frame and structure with stone cladding. There is some metal stud work but most of the building was modular and delivered in sections to be put together. think of it as a giant kit house.. I have put an endoscope in the voids but not seen anything as yet that is 100% the linked path. There is one water pipe around 2 metres in length entering the flat then the water and heating are all plastic pipes. with the boiler outside the flat door in a cupboard.
Given the nature of the building its not wise to start pulling bits apart and making holes into wooden joists etc..
Its clearly been there since it was built.
What would you put on certificate to indicate this... I have put so far ... shared parallel earth path between circuit x and y. location not known due to nature of building.

Any thoughts or advice
 
It hasnt stopped me taking the tests I was merely checking whether to record it or not, given it was such a new installation i was a bit surprised to find one. Come across plenty in older homes not many in new. my only real concern was the possibility of joined circuits on line and neutral but i had ruled that out already. so just peace of mind really.
 
It's common for CPCs to be interconnected for whatever reason, be it by design or by accident, think supplementary bonding. Seen CPCs joined at the end of circuits to bring down Zs of both as well.
 
Could be supplementary bonding or both the metal boxes touching metal stud. Take it the insulation resistance testing was ok? I would do a R1 +R2 test on both circuits removing C.P.C. from earth bar.
 

Reply to Parallel earth path between 2 circuits in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
689
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
657

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
974
  • Question
We just left it as it was, again the customer didn't seem too bothered, dont think she wanted me digging any further.
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top