Is this a big no no (I suspect it might be)?

Here is the situation (this is for stage lighting, so not a domestic building):

We have a 63A isolator going to a consumer unit (I presume with a 63A main switch, I didn't make a note of it). From here we have a 20A MCB wired to 12 fused switches (all with 13A fuses at present). From each switch we have 2.5mm twin+earth cables running about 15m, partly in conduit, partly in free air. These cables are then connected (not sure by what method) to a pair of 18 multicore cable (approx 20mm outer dia, guess it's either 1mm, 1.5mm or 2.5mm cores) - so each multicore has L,N,E from each switch (i.e. 6 circuits on each). This runs for about 5m before breaking out into individual 1.5mm pvc flex.

What we would ideally like is to have a single 42A :eek: supply where the multicore breaks out. Clearly this isn't going to be possible using the existing cable. But would it be possible to pair up some of the 2.5mm twin+earth, then multicore circuits to get a single supply higher than the existing 13A? 26A to 30A would be nice. So we'd bypass the switches, connect two lots of 2.5mm to a new mcb, and then at the other end connect the corresponding 2x L & 2x N to form a single supply.

Is this an allowable configuration, even if not typically reccomended? If so, what would be a max current we could get from this supply? Going even further, could we parallel up 3 lots of cable to get even more current carrying capacity?
 
Typically, a lighting( pro rig) will have 1x 50/63a supply so easy to plug in to an already installed, linked together... 63amp supply. That is the norm. Sometimes bands have several lighting rigs which are linked using 13a plugs, so usually relying on a 32amp ring main breaker. The host's breaker may trip as it should. Many bands make up there own lighting rigs, often times over the capacity of the protection. There is no way round this, unless the host provides a 63amp connection.

Many times stage 'disruption' is because of over current demand....even some pros think they can plug into the mains via a 13a socket, and then wonder why all the lights have gone off....stage lighting is hungry
 
Thanks for your reply. I'm still not sure if I can parallel up multiple twin + earth cables? This is for a semi permanent installation - we don't have to worry about bands bringing their own lighting rigs.
 

Reply to Paralleling cables in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
920
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

David Savery visits the Viperclip stand in his latest video. Skip to 29:15. He also visits Hager to discuss their AFDDs but isn't welcomed!
Replies
10
Views
2K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
779

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top