I'm currently working at a small bakery conversion which has a flat above it. I want to use it as one of my jobs for my upcoming self certify assessment. I was told by the baker that he had been advised by the oven manufacturer that he needed a 63amp supply and this is what I quoted for. A supply and isolator were fitted by me weeks ago but the oven has turned up and it is rated at 85amps. The guy who sells the oven says they never run at anything near this which is why he advised our customer that only a 63amp supply was needed.
This is only my second assessment, but I want to be sure that it's something that it is something I should use as a job or not. The customer asked for 63amp 3 ph supply, I have given 63amp. The circuit isn't unsafe. The cable is more than protected. If the seller of the oven is right (probably taking into diversity, I don't know) then it will run fine and never trip.
I am worried though that the examiner will say why have you designed it for only 63 amps when the oven takes 85?
I've read the OSG and it says that diversity only applies to domestic ovens. However I will say that this oven is actually 5 ovens in one, kind of like lots of pizza ovens on top of each other so they will be kicking on and off all the time.
Any thoughts? Will the examiner agree with ' well the customer asked for it, you gave it and what you gave is safe'
This is only my second assessment, but I want to be sure that it's something that it is something I should use as a job or not. The customer asked for 63amp 3 ph supply, I have given 63amp. The circuit isn't unsafe. The cable is more than protected. If the seller of the oven is right (probably taking into diversity, I don't know) then it will run fine and never trip.
I am worried though that the examiner will say why have you designed it for only 63 amps when the oven takes 85?
I've read the OSG and it says that diversity only applies to domestic ovens. However I will say that this oven is actually 5 ovens in one, kind of like lots of pizza ovens on top of each other so they will be kicking on and off all the time.
Any thoughts? Will the examiner agree with ' well the customer asked for it, you gave it and what you gave is safe'