BigSi

-
Joined
Jul 29, 2009
Messages
251
Reaction score
55
Location
Cornwall
Hi guys.

As the title says really. I know installing a new circuit, in this case feeding a garden shed, falls under the scope of Part P. And that replacing a damaged cable on a like-for-like basis isnt, but what about replaceing a length of 6242Y (laid on a flower bed feeding a garden shed), with a more suitable SWA cable?
 
You don't replace like for like if the original is not suitable for the environment, with regards to BS7671 the concerns in a garden are UV tolerance, water ingress, mechanical damage etc etc .. the very fact the 6242y has been damaged to an extent it requires replacing is evident it is totally unsuited to the install. Swa will be more suited but thought is still required as to the routing of it with regards to garden tools etc, avoidable damage to the sheath could lead to corrosion of the steel wire.

Just note here you can't make a waterproof repair as the existing doesn't comply even to the reg's under which it was installed or to any reg's even in my 26yrs so you are in fact making a circuit alteration by replacing a section of it thus must comply to 17th.

Edit .... ignore the lengthy explain if you were just asking if it was notifiable but regardless it does express what needs to be done to comply... sorry if teaching you to suck eggs i misread you post if this is the case
 
Last edited by a moderator:
I shall not even try and answer the question,even if there was a remote possibility that I could with any sort of confidence

So,after many years of the nonsense,here we have a question on the relevance of Part P on an electricians forum where the subject impacts on the trade more than all other trades and yet, even on here, after all these years, this Part P nonsense remains confusing

If us people working in the trade are confused,how much more confused be the GENERAL PUBLIC

Its no wonder its ignored and by-passed,its a turkey and it needs stuffing,its a shame that its just the turkey that is gone by Christmas
 
Hi guys.

As the title says really. I know installing a new circuit, in this case feeding a garden shed, falls under the scope of Part P. And that replacing a damaged cable on a like-for-like basis isnt, but what about replaceing a length of 6242Y (laid on a flower bed feeding a garden shed), with a more suitable SWA cable?

Part P notification for work outside is longer required - only applies to rooms with baths or showers or new circuits.
 
Thanks guys.


I had an inkling that it wasn’t notifiable, but just wanted some reassurance.


You don't replace like for like if the original is not suitable for the environment, with regards to BS7671 the concerns in a garden are UV tolerance, water ingress, mechanical damage etc etc .. the very fact the 6242y has been damaged to an extent it requires replacing is evident it is totally unsuited to the install. Swa will be more suited but thought is still required as to the routing of it with regards to garden tools etc, avoidable damage to the sheath could lead to corrosion of the steel wire.

Just note here you can't make a waterproof repair as the existing doesn't comply even to the reg's under which it was installed or to any reg's even in my 26yrs so you are in fact making a circuit alteration by replacing a section of it thus must comply to 17th.

Edit .... ignore the lengthy explain if you were just asking if it was notifiable but regardless it does express what needs to be done to comply... sorry if teaching you to suck eggs i misread you post if this is the case


The 6242Y was existing and certainly not suitable for its intended use. That cable was removed straight away, and a nice shiny length of SWA (with external glands) cleated to the wall running behind the flower bed. I did ask who originally installed it, to which he replied ‘Oh, an electrician’....me thinks he was lying!
 
Are you sure this is not notifiable - after all you are changing the characteristics of the circuit (it is not a direct cable replacement as in after a mouse chews through a ring cable)...

But then is it really worth worrying about?
 

Reply to Part P or not (replace cable from 6242Y to SWA). in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
424
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
726
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
891

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top