Pat testing of110v 50meter 2.5mm extension reels they are brand new can I pass them or do I have to cut them in half so they are 25 meters long ??? Help
 
Put it like this IF you cut my nice shiny new extension leads in half i would never give you any work again, either pass them or omit the from the tests, you really cant chop them!
 
Page 79 of CoP states maximum recommended lengths NOT RCD protected. Stated lengths can be exceeded if RCD protection is provided.

Do you agree?
 
Page 79 of CoP states maximum recommended lengths NOT RCD protected. Stated lengths can be exceeded if RCD protection is provided.

Do you agree?

Not totally

Why would you put an RCD on a 110v supply if these leads are used on tool transformers with the secondary centre tapped to earth the voltage to earth would only be 55v
 
The volt drop over 50 mtrs on 2.5mm and 110v supply would be 5.50 volts (5%) if it is operating an appliance drawing a maximum of 672 watts, anything over 672 watts it would need to be stepped up to 4mm. I think this is right, but don't take my word for it I'm probably way out! lol
 
No need for an RCD, Im guessing the reel extension will be used on site so running from a Generator..... The site lighting is designed to be daisy chained over 100's of meters, I shouldn't worry about it, as long as you're earth continuity readings are below the expected maximum, then pass it.. As a general rule of thumb, I use .01 Ohms per 3-feet of flex... this would give you a max reading of something stupid like 16 Ohms, but you'll end up taking a reading somewhere between .28 - .47 Ohms I imagine.

The most important checks on these is visuals on the trailing sockets/plugs, visuals on the primary insulation for damage, and condition of the pins/connectors as well as terminal connections within the plugs/sockets.

RCD's for leads over 30 metres are for 240v supplies, and factored in because in effect you are extending the ring final/radial circuit by 30 meters more than the original design allowed for.
 

Reply to Pat test of 50mtr 2.5 mm ext reels in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
771
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

  • Question
throw the phone down the moment they mention PAT testing !
Replies
5
Views
2K
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top