NeilC
Hi,
I have a Metrel BetaPAT Plus MI 3304 Tester and whilst at a loose end, I browsed the autotest codes in the manual. Big mistake! I am now doubting myself in terms of testing IT appliances correctly and would appreciate your views on this please.
I thought an Earth Bond (200mA), Insulation (1Mohm, 250v, 3s) and leakage (3.5mA) was correct? (complies to EN 60950).
When reading other testers comments, they do not appear to power the PC up i.e. run the leakage test?
According to the Metrel Autotest codes the EN 60950 test is - Visual, Earth Bond (200mA), Insulation (1Mohm, 250v, 3s) and SUB leakage ((3.5mA) which will not power the appliance up of course).
What tests do you do on a tower PC, for example?
Thank you in advance
Neil
I have a Metrel BetaPAT Plus MI 3304 Tester and whilst at a loose end, I browsed the autotest codes in the manual. Big mistake! I am now doubting myself in terms of testing IT appliances correctly and would appreciate your views on this please.
I thought an Earth Bond (200mA), Insulation (1Mohm, 250v, 3s) and leakage (3.5mA) was correct? (complies to EN 60950).
When reading other testers comments, they do not appear to power the PC up i.e. run the leakage test?
According to the Metrel Autotest codes the EN 60950 test is - Visual, Earth Bond (200mA), Insulation (1Mohm, 250v, 3s) and SUB leakage ((3.5mA) which will not power the appliance up of course).
What tests do you do on a tower PC, for example?
Thank you in advance
Neil