Setting up a temp site board in a little brick bunker, DNO haven't supplied an earth as its an out house.
So I've installed a rod and am getting a Ze of 44.7 ohms.
Now my PEFC and my PSCC are both 5A's.
Why are they the same as its now TT? Should they be the same
.
Should'nt the PSCC be the greater of the two on a TT or not ?
Are there problems with having a really low PFC ?
Whats your thoughts on this, and could someone explain it to me.
Thanks.