steve.t.

Hi
just doing some tests on a tt instillation, will be doin 2392 shortly. getting 1A on PEFC, can anyone explain this. the Ze is 174.
Any help would be great thanks
 
Hi
just doing some tests on a tt instillation, will be doin 2392 shortly. getting 1A on PEFC, can anyone explain this. the Ze is 174.
Any help would be great thanks

If you think about how you are deriving PEFC on a TT system, by Ohms law, the value will be quite small.

In your case with an Ra (not Ze) of 174 Ohms, a calculated PEFC would be 230/174 = 1.32 Amps so not too far away.

Of course PSSC will be much higher and will therefore become PFC.
 
Good Response IQ...

oh and with a rod reading of 174 i would be slightly concerned about proximity to the 200 mark...!
 
Yes, depth is king, I'd take a deeply driven rod (oooh matron!) with an Ra of 500 Ohms over a short rod at 100 Ohms, reason being the deeply driven rod will be virtually immune to soil drying/freezing so is highly unlikely to approach the true maximum of 1667 Ohms (assuming 30mA RCD protection)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Pefc
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
5

Thread Tags

Advert

Thread statistics

Created
steve.t.,
Last reply from
IQ Electrical,
Replies
5
Views
2,211

Advert

Back
Top