Hey guys,
Doing a periodic, and have found a spur taken off a 30A 2.5mm ring final circuit. The spur feeds 3 sockets in the kitchen that are rarely used for anything but one of them is used for the kettle. The problem being that the spur is wired in 1mm cable! Also this spur spurs off (5A fused this time) to provide under cupboard lighting. All death and energised tests are well within acceptable parameters.
I am inclined to give it a Code 2, and recommend that the cable be replaced with 2.5mm, but would welcome any views.
Cheers in advance.
Matt
Doing a periodic, and have found a spur taken off a 30A 2.5mm ring final circuit. The spur feeds 3 sockets in the kitchen that are rarely used for anything but one of them is used for the kettle. The problem being that the spur is wired in 1mm cable! Also this spur spurs off (5A fused this time) to provide under cupboard lighting. All death and energised tests are well within acceptable parameters.
I am inclined to give it a Code 2, and recommend that the cable be replaced with 2.5mm, but would welcome any views.
Cheers in advance.