Hi there i was wondering what code you would give for charred black and melted insulation on line conductor at termination point in fuseboard? the circuit is feeding a wall mounted heater in 2.5mm T and E cable protected by a 3036 15 amp fuse. Is it caused by loose connection what action would you take? Thanks
 
personally, as long as the fuse carrier teminals are undamaged, i would re-terminate it, extending with crimp if necessary. left as is, it is IMO a fire hazard and should be given at least a code 2 if not a code 1.
 
As it is, code 1.

I don't think it should be left like that, even if you are 'only doing a PIR'. It's clearly overheating and presents a danger.

It probably is a loose connection. Have you tried the connections?
Fix as Tel said.
 
[ElectriciansForums.net] periodic coding

Got a new DB out of this as you can see the the damage third from the end and then check the cable on the end fuse. But on another job I got called out by the a letting agent found the exact same problem with the immersion circuit so as a temp I doubled up the lighting circuits to one fuse and made safe the immersion circuit to another fuse then put a cost in for new DB the only thing is that was 2 months ago and me thinks they have give the job to the I&T company who passed the board fit via a PIR 6 months earlier only problem was the damaged was long term in the DB ??? A well there you go.

Also the useall culprits for these types of faults that I have found is Shower,Cooker and Immersion circuits
 

Reply to periodic coding in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There is no homework, and I'll never see these photo again.
Replies
3
Views
618

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top