Periodic inspection report help needed | on ElectriciansForums

Discuss Periodic inspection report help needed in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

D

dandawson1983

Hi I have recently come across a property with questions I need an answer for and I hope the more experienced sparks can help. The property has an old consumer unit with no rcd protection and 3036 fuses. The boiler is wired in 2.5 t and e on a 5 amp breaker! The downstairs lighting is run in metal conduit in singles with no backboxes to light switches and twin cable to light fittings with no earth. The upstairs lights have an earth at each light but a constant low voltage of around 50-70 volts is present with lights on or off. Could this be to do with induced current or a borrowed neutral? Also no cooker circuit present however kitchen is on own ring and cooker plugged into socket ( also no cooker switch present because of this). If anyone could help out with any of this and any codes for the above I would be extremely grateul. Also if no earth present on downstairs lights I assume I can't do test readings for the periodic on that circuit!
 
Boiler on a 5A breaker is no problem on the assumption that there is a FCU with a 3A fuse in it for the boiler controls. Wooden back boxes would get a code 2 IMO. On the upstairs lighting, what are you measuring between to get the 50-70V? Regarding testing the downstairs lights the only test you can do is a IR between L and N and comment on the lack of CPC giving it a code 4 so long as no Class 1 fittings are present. Finally, what is the rating of the cooker?
 
If you google the no earth on lighting mate theres a guide from C@G i think about what to do, I had/have it as PDF if i find it i ll send it on to you.
 
measured between live and earth and live and neutral on voltage setting as tried to do my zs on each light and it will not register because of the low voltage. also light fittings are ancient so assuming they will be class 1.
 
Hi when doing a pir i found on zs test that sockets were 1.2 ohms is this ok cos max zs in bs7671 32amp breaker is 1.44ohms why do you have to mulitply by 0.8?? to get 1.15ohm cheers
 
you multiply by 0.8 to allow for increase in resistance with temperature rise. so your reading is borderline. probably either a spur off the ring or poor connections.
 
Hi when doing a pir i found on zs test that sockets were 1.2 ohms is this ok cos max zs in bs7671 32amp breaker is 1.44ohms why do you have to mulitply by 0.8?? to get 1.15ohm cheers

If the circuit is protected by a 30mA rcd then it is fine as you can take 1667Ω as your max. If not then it is probs a case of finding poor connection, although upgrading main earth and or tails (if appropriate) could also be just enough to improve your 1.2Ω reading.:)
 
i also dont know much on the voltage drop side of thing how do i work it out ??
also when measuring the pscc what sort of reading should you get and what if ze is too high??
do you have to install an isolator on cable if main head is more than 3meters away from meter??
 
Hi when doing a pir( I assume that your a competant person then or even an electrician) i found on zs test that sockets were 1.2 ohms is this ok cos max zs in bs7671 32amp breaker is 1.44ohms why do you have to mulitply by 0.8??(you don't know this and your doing a PIR) to get 1.15ohm cheers

i also dont know much on the voltage drop side of thing how do i work it out ??( is this a general question as VD is something you would do at the design stage, or if there was a problem with an appliances)
also when measuring the pscc what sort of reading should you get and what if ze is too high??(why would the Ze be high, what would you expect the Ze to be)
do you have to install an isolator on cable if main head is more than 3meters away from meter??(normally yes)[/QUOTE]

Can I ask do you feel competant enough to do PIR work after what really are basic questions.
 
i also dont know much on the voltage drop side of thing how do i work it out ??( is this a general question as VD is something you would do at the design stage, or if there was a problem with an appliances)
also when measuring the pscc what sort of reading should you get and what if ze is too high??(why would the Ze be high, what would you expect the Ze to be)
do you have to install an isolator on cable if main head is more than 3meters away from meter??(normally yes)[/QUOTE]

Can I ask do you feel competant enough to do PIR work after what really are basic questions.

HI i am an electrician but have not done my 2391 yet. i have been collage but they dont teach you much just to pass the exam i am trying a pir at home to get use to it and i thought i would ask some questions that iv had diffrent asnwers for.
is this a crime??
alot of people just write down results and dont now why that are what they are!! not everyone has the experience like others that why it is useful on here. we dont need sarcastic comments just trying to lean!!
 

Reply to Periodic inspection report help needed in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
814
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
873

Similar threads

  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K
Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Replies
14
Views
677

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top