Hello all.
When conducting IR tests on condition reports, with L-N connected together and testing to earth. What equipment have you found will still cause the readings to be 0.00?
Did you switch off the main switch or just the MCB's?
Tested with main switch off.I hope the answer will be the Main Switch with a dirty great big lock on it
Just had another look in this board, didn't realise there was a neutral link behind the main switch cover. It's a been converted to single phase from three.
So with the main neutral disconnected this time, testing the same way as before and testing each circuit individually I'm getting 0.23 on every circuit.
A couple test greater than >999 L-E but L with N together to E was 0.23.
Whats your thoughts fellas?
Just had another look in this board, didn't realise there was a neutral link behind the main switch cover. It's a been converted to single phase from three.
So with the main neutral disconnected this time, testing the same way as before and testing each circuit individually I'm getting 0.23 on every circuit.
A couple test greater than >999 L-E but L with N together to E was 0.23.
Whats your thoughts fellas?