Hello all.
When conducting IR tests on condition reports, with L-N connected together and testing to earth. What equipment have you found will still cause the readings to be 0.00?
 
Hello all.
When conducting IR tests on condition reports, with L-N connected together and testing to earth. What equipment have you found will still cause the readings to be 0.00?

None, unless it's faulty.

An RCD spur or RCD socket can give a low IR measurement to earth, but not 0.00 Mohm.
 
Where in the install did you do the IR test? At the board I hope. If tested correctly then there is a fault. Test L-CPC and N-CPC to eliminate one or the other.

If it was tested at a socket etc then even with MCB open think PME could be the cause.
 
Well sounds like an appliance or the circuit has got an earth fault. Needs sorting.
 
Just had another look in this board, didn't realise there was a neutral link behind the main switch cover. It's a been converted to single phase from three.
So with the main neutral disconnected this time, testing the same way as before and testing each circuit individually I'm getting 0.23 on every circuit.
A couple test greater than >999 L-E but L with N together to E was 0.23.
Whats your thoughts fellas?
 
Just had another look in this board, didn't realise there was a neutral link behind the main switch cover. It's a been converted to single phase from three.
So with the main neutral disconnected this time, testing the same way as before and testing each circuit individually I'm getting 0.23 on every circuit.
A couple test greater than >999 L-E but L with N together to E was 0.23.
Whats your thoughts fellas?

Further investigation needed.
 
Just had another look in this board, didn't realise there was a neutral link behind the main switch cover. It's a been converted to single phase from three.
So with the main neutral disconnected this time, testing the same way as before and testing each circuit individually I'm getting 0.23 on every circuit.
A couple test greater than >999 L-E but L with N together to E was 0.23.
Whats your thoughts fellas?

Is this with each final circuit neutral disconnected and line disconnected (or circuit breaker opened)?
 

Reply to Periodic IR testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
344
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top