Hi

Have done PIR of church today.
There are quite a few lights at high level, more than 30 feet off the ground. There are pews in the way and I cant get up to them even with a tower although someone has installed them off a ladder or with full scaffolding at some stage. There are also some metal chandeliers about 15 feet up I did R2 readings which were OK.

I cant really do Zs reading on these or heaters which are 20 feet up. The risk of shock is effectively zero as they are all wired in MICC and nobody is going to be able to touch them when they are energised.

Do I have to do Zs readings.

Thanks
 
and then just make a note on the certificate? I guess if you cant get up to do a zs then you cant get up to do a r1+r2 other wise could have done zs by calculation
 
You can list as many limitations as the client will agree to, each one reducing the value of the PIR.

Did you not survey the church prior to pricing/receiving the order?

You will be omitting continuity of protective conductors, earth fault loop impedance and polarity on these circuits, also omitting any level of detailed inspection on these light fittings.

I'd have allowed for a scaffold and completed the task.
 
Have only done periodic in domestic dwelling so far and quoted for them remotely as the general range and structure of such buildings are generally standard, but would agree that a survey should be done for such buildings before quoting.
 

Reply to Periodic - Lights at height in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

Similar threads

Thank you so much for your help with this light work perfect now thank you again much appreciated
Replies
2
Views
327

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top