Just been to a domestic property and filling out pir now with some querys
An old ELCB fitted in this premises which of course we couldnt test except but pushing the test button
my query is what do i write down for max zs allowed on this or just write max zs for each 60898 mcb that is fitted.
Also for rcd trip times just fill as a limitation?
No other rcd protection except this fitted at present
TT Spike 189 ohms which will be suggesting to replace as location is unknown