J
jambogee74
Hi I done a periodic on a house to be sold. According to present owner it was rewired 15 years or so ago. Only problem is that it has a very old fuseboard at present and the wiring is PVC but stranded. All circuits gave good readings though using existing conduit as an earth. Readings where in the region of 0.28 ohms to 0.47 ohms. Now the question is? A to rewire would be a major job so as reading are ok is it best to leave be?
B do I replace the board for new but incorporate the conduit to give best earth readings possible.
If it was a house they where to carry on living in I would suggest a rewire but its not. Any suggestings??
B do I replace the board for new but incorporate the conduit to give best earth readings possible.
If it was a house they where to carry on living in I would suggest a rewire but its not. Any suggestings??