P

pushrod

I know that often people will just test PSCC as that should be higher than PEFC so test between L1 - N, L2 - N and L3 - N then take largest value double it and record that value. However was looking through the user guide for the 1552 and noticed that you can test phase-phase pfc. Does this mean that you would just test L1-L2, L2-L3, and L1-L3 and just record the highest value ie not double it.
If correct would you be allowed to do this in a 2391 exam (it would be more accurate?) or do they prefer the L-N and rule of thumb double method.
cheers
 
The biggest fault current you will get on a 3 phase circuit is phase to phase. Yes test phase to phase even on your 2391-10

I don't know if it's a centre specific rule but the 2 centres that I do 2391 pre-exam refreshers for strictly forbid line-line PFC measurement on the practical, even though the instruments are capable.
 
I don't know if it's a centre specific rule but the 2 centres that I do 2391 pre-exam refreshers for strictly forbid line-line PFC measurement on the practical, even though the instruments are capable.

You maybe right now IQ I did my 2391 a fair few years ago, and then we took it phase to phase, it may have changed since. If that's the case then appologies pushrod for giving false information.

Saying that though in real life I would take phase to phase on a PSCC test as that is liable to give you your biggest fault current.
 
Also, if a Zs can't be measured with the BS 1363 lead, it must be calculated-it's all becoming rather pathetic!
 
Also, if a Zs can't be measured with the BS 1363 lead, it must be calculated-it's all becoming rather pathetic!

That's our friends from the NICEIC doing, all the statutory documents recognise that at certain times live working is unavoidable and sometimes neccessary, just ask the DNO guys about live working. Live testing is a recognised discipline. I want to take my Zs live with all those parallel paths, as that will be the condition of the installation when a fault occurs, not on a piece of paper.
 
Thanks guys for the info - suppose i'll just have to ask what they want - i have a feeling that the only live testing being done is Ze, PFC and i think an rcbo via a plug lead - (not even certain about that) just a few nerves before the test.
 
NIC-EIC guide states that Unless the test instrument is designed to operate at 400v then the pfc is to be calculated chapter 7 or 8 Inspection testing and certification
 
i would take just one phase test then times by 1.8.all line supply,s would have same resistance or should do.and i agree live testing is a must and also helps with polarity test.it say,s measured zs not calculated
 
i would take just one phase test then times by 1.8.all line supply,s would have same resistance or should do.and i agree live testing is a must and also helps with polarity test.it say,s measured zs not calculated

Guidance Note 3 says to multiply by 2 as we're not to be trusted with 1.732!
Where fo you get 1.8 from?
 
hi when i did 2391 in june was just told to measure between lines and neutrals and multiply the highest by 2 as they dont like you measuring between the lines even though the megger says you can and calculate all Zs except for sockets
the Ze or Zdb at the single phase is also the Zs for the circuit supplying the single phase from the three phase if that makes any sense lol
 
hi when i did 2391 in june was just told to measure between lines and neutrals and multiply the highest by 2 as they dont like you measuring between the lines even though the megger says you can and calculate all Zs except for sockets
the Ze or Zdb at the single phase is also the Zs for the circuit supplying the single phase from the three phase if that makes any sense lol

That's exactly the same as we teach it, namby pamby calc's!
 

Reply to PFC on 3 phase with a megger 1552 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

  • Question
I believe that it is incorporated into the 5 days. But will double check. Thanks.
Replies
6
Views
990
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top