Hi,
I have recently tested a new installation i have completed on a domestic property. All the relevant tests were completed and verified as ok. However the PFC reading was > 10ka.
My Fluke test instruments only give a greater than value if 10ka is exceeded, so I do not have the actual reading.
The system is a TNCS
with readings of:
Ze: 0.11
even measured the Voltage just to be on the safe side:
V : 245

Obviously the calculation using these two measurements would suggest that the pfc is below the breaking capacity of my mcb's as it would be around 2.2ka.

Can anyone shed any light on this, or suggest any methods on how to acheive a lower reading (other than moving the house further from the source) ?????

Cheers
Alan.
 
I would suggest that you meter is on the wrong setting or needs calibrating/repair.

I took some readings earlier today: Zs 0.16 Pfc 1.29 kA. This is fairly standard for a domestic.

You would need to be right on top of the sub with huge incoming cables to achieve >10kA. Only happens in factories etc in my experience. Anyway - if you ring the NICEIC they will say that the breaking capacity of the HRC fuse (BS1361) will protect the entire installation - that is why we can let rewireable fuse boards off the hook when performing a periodic.

Hope that helps.
 

Reply to Pfc reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top