A
ala
Hi,
I have recently tested a new installation i have completed on a domestic property. All the relevant tests were completed and verified as ok. However the PFC reading was > 10ka.
My Fluke test instruments only give a greater than value if 10ka is exceeded, so I do not have the actual reading.
The system is a TNCS
with readings of:
Ze: 0.11
even measured the Voltage just to be on the safe side:
V : 245
Obviously the calculation using these two measurements would suggest that the pfc is below the breaking capacity of my mcb's as it would be around 2.2ka.
Can anyone shed any light on this, or suggest any methods on how to acheive a lower reading (other than moving the house further from the source) ?????
Cheers
Alan.