S

solavie

when doing a PFC test on the lighting circuit, it keeps tripping the MCB type B . Also had problem with testing the fault current where I get trip on my meter. Using a Megger MFT 1552 for both test. Any suggestion as to why.

Thanks
 
the meter delivers a high current for a short period of time and will trip a 6amp type b
this is normal and not a fault you can calculate or use a type c for testing purpose
then replace your type b
 
I have just changed the consumer unit and was doing all the nornal test. I thought that I had to do a PFC test to check the MCB capacity to withstand. I am fairly new in this field.

My Other problem was the ze where I keep getting trip on my MFT 1552. I can work it out but would really know why the meter trip. I was using the 3 test lead and setting the meter on no trip as suggested by the instruction.

Cheers.
 
pfc and pefc is done at the cu put the dial pfc use two leads red in red socket green or black in black socket(not no trip)socket test line and neutral for pfc line earth for pefc record highest of the two the ka resault should be lower than whats on the side of the breaker
 
You would measure your PFC at the point where this would be at it`s highest level. i.e. the consumer unit.
When you know this value you check to see that the installed equipment i.e. fuses/mcb`s etc, can cope with this level of fault current.
If you are measuring PFC at the circuit extremity then the value would be lower. As old dog said you probably meant Zs.

How did you connect your test leads when you were trying to measure Ze
 
diditrain

Connected red lead to phase, green to cpc and black to neutral at ceiling rose. Set meter to Loop No trip. Then got trip on test meter but no trip at consumer unit.
 
hi wile i was testin pfc and pefc i got a reading of 3.5 on a TNC-S system would this be acceptable any help would be great cheers

thts testin pssc and pefc cheers
 
Last edited by a moderator:
there is a way to calculate it pfc if ya got ze and visa versa i thought normaly on a tncs system the pfc is 1600ka to work out ze im i rite in sayin ohms law 230/1600 = ze 0.14 with a readin of 3.5 would i do the same thing 230/3.5???
 
i just know when i go for me assesment the guys gona ask me y we test for pfc and ze do all the breakers have to fall with in the pfc value???

would i record 3500Ka on both parts of the eic cert???
 
Last edited by a moderator:

Reply to PFC test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
752

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
486

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top