F

fixit4u

Hi, anyone who can briefly explain to me how a reading at a 3-phase board on the pfc can be said to be " quite satisfactory " being show as >19.9ka

the zs at the dist board was 0.01

i phoned an experienced test engineer about my reading as i have not come across one this high before and he said it is quite ok and write it down but could not explain to me why a reading like this would be,i have only come across readings such as 3.6ka 4.1ka etc and never >19.9 and would like to know why a reading like this is ok ?

many thanks for any replies.
 
Well theres nothing bad about it, you have an excellent earth. I suppose the only problem you could have is the maximum breaking capacity for the protective devices as the PFC is unbelievably high. What type of fuses are in the main cut out? The place must be sitting on a substation for a reading like that :D
 
Hi, anyone who can briefly explain to me how a reading at a 3-phase board on the pfc can be said to be " quite satisfactory " being show as >19.9ka

the zs at the dist board was 0.01

i phoned an experienced test engineer about my reading as i have not come across one this high before and he said it is quite ok and write it down but could not explain to me why a reading like this would be,i have only come across readings such as 3.6ka 4.1ka etc and never >19.9 and would like to know why a reading like this is ok ?

many thanks for any replies.

Beacuse your relying on the suppliers protective device to cover the PFC?

And if anybody can give a definate answer I'll be learning something aswel, so thankyou in advance..:D
 
Hi. PFC is derived by dividing the Voltage by the resistance- so your results re not that far out.. Do remember thouigh that the PSCC on 3-phase is rouighly twice the single phase value...--Are you sure zs is 0.01, if so then you are definately relying on back up protection upstream as already posted.
 
is it not only in an extreme situation that pfc would occur that high , and does this surely mean that the breakers will all trip in the quickest possible time, so it must be a good thing
 

Reply to Pfc testing result in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
  • Question
In the mind of someone lying there wide awake at 3AM, just about anything.
    • Like
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top