today i was doing inspection and testing of a large building with 26 boards.
the part i was doing had 3 DBs about 60 m away from mains inlet and one of the boards is on a 100A supply with 25mm 4core 3ph cable which i think is to small well for VD any way because some runs from the DB are a further 50m.(seperate earth cable 16mm) what do you think?from this board im getting 11KA phase to phese (L1 -L2 -L3).
is this pfc ok the MCB are rated at 10KA or they are note effcted by pfc.
and the other DB pfc is <19.9 phase to earth which is to much i still have to double it for 3 phase.
i dont know what the mains fuse is yet but it has to be a bs 88-2.1 or a bs 88-6 .
am i right? and what could i do to solve this problem this is a grey area for me because i have never been off the scale on my tester .
thanks
the part i was doing had 3 DBs about 60 m away from mains inlet and one of the boards is on a 100A supply with 25mm 4core 3ph cable which i think is to small well for VD any way because some runs from the DB are a further 50m.(seperate earth cable 16mm) what do you think?from this board im getting 11KA phase to phese (L1 -L2 -L3).