Hi i am after a bit of advice, I measured pfc at a domestic ccu & got 3.8kA. (PME) Push button breakers 3871 are used for the storage heater board which have a lower breaking capacity that the pfc measured. At the main ccu there were 3036 semi enclosed which are rated around 1 to 2 KA. My question, is this acceptable? I have found in the BGB reg number 434.5.1 which i am assuming this means as long as there is a cutout fuse it's o.k.

Cheers
 
Domestic consumer units are designed to be an assembly that can have up to a 16kA fault current so long as they have a BS88 /BS1361 main fuse.

This is in the (red) OSG 7.2.7 prospective fault current, not sure where it is on the green OSG, just look up fault current.

When the 3036 ones go they will spray metal very nicely, but be safe (ish)!
 
Hi i am after a bit of advice, I measured pfc at a domestic ccu & got 3.8kA. (PME) Push button breakers 3871 are used for the storage heater board which have a lower breaking capacity that the pfc measured. At the main ccu there were 3036 semi enclosed which are rated around 1 to 2 KA. My question, is this acceptable? I have found in the BGB reg number 434.5.1 which i am assuming this means as long as there is a cutout fuse it's o.k.

Cheers

No, it's no right, Annex Za won't apply in your case.
 
Cheers Richard, I am not too bothered about the 3036's, i am more concerned with the push in breakers whether they can safely interrupt the fault current.
Can you please explain Chris?

Cheers
 
Last edited:
If you have only 3036's, then it will not comply, as their short circuit capacity is lower then your PFC.
If you have BS1361/BS88 upstream, which have a 16kA/33kA (CBA looking it up) breaking capacity, then it will comply, due to the Reg you quoted (434.5.1).
 
Cheers, for replies i have had it confirmed. Regulation 434.5.1 cover's domestic situation's where fault current is too high for the ocpd as long there is cutout fuse which is normally rated at 33KA (BS 1361 type 2)
 

Reply to pfc in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
514
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top