Hi,
Has anyone ever experienced the following issue on a single to theee phase convertor. The issue only seems to be on initial startup in the morning, initial soft start is ok then change over, it sounds like its single phasing then the supply breaker trips. After 5 attempts it works ok and once a bit of warmth itll work all day. I shall mega the motor/generator first thing tomorrow but any suggestions much appreciated, as the supplier/manufacturer is now closed till Monday
you sure your soft start is working? Had a similar issue with a dc convertor. The soft start would try to start but not switch in time. three more attempts then it would actually ramp up properly.
You could try and meg the motor both cold and also when warmed up. Just to check there is nothing that is changing character on the load side.
Reply to Phase convertor issues in the Talk Electrician area at ElectriciansForums.net
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
4K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...