Im inspecting and testing a photo studio where there will be staff working there.

There is a 3 phase Distribution board with no RCD protection.

Do all the breakers have to be changed to RCBO's
 
no, in myopinion, it wont fail inspection if the circuits dont have rcd protection, escpecially in commercial environment, if you do have rcd it might trip every day
 
Not if this installation was prior to the 17th edition which i take it is as you are doing a PIR. Thing that would need additional protection by RCD are socket outlets that may be used for portable handheld equipment outside the equipotential zone. All other instances of lack of RCD's would only be coded 4.
 
I wouldn't think it would fail either, but note it under your oberservations/ recommendations box (on the test cert) that you would recommend the change.
 
I wouldn't think it would fail either, but note it under your oberservations/ recommendations box (on the test cert) that you would recommend the change.

Why would you recommend it be changed if it complies to the edition of the regs to which it was designed and installed?
 
no, in myopinion, it wont fail inspection if the circuits dont have rcd protection, escpecially in commercial environment, if you do have rcd it might trip every day

commercial enviroments should be RCD protected , to quote the RCD may trip every day , if there is a fault may , i have a heavy industrial site which every circuit is RCD protected and it never trips unless there is a fault .

I agree with sintras post 100%
 
Why would you recommend it be changed if it complies to the edition of the regs to which it was designed and installed?

Hi Sintra, Yeah I know what you are saying... Would still be noted in the obeservations box right? But I'm wrong in saying you'd recommend the upgrade to a modern equivelant? Sorry if thats misleading info :(
 

Reply to photo studio 3 phase board with no rcd protection in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Think all has been covered already, but echo-ing the above if I was getting my DB swapped and had a 3 phase head, I would put a little TPN board...
Replies
5
Views
386
What makes it a lack of space? I’d say to the customer to dismantle a cupboard or whatever to creat the space you need for the extra equipment...
Replies
1
Views
228

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top