what is DNO??
i thought if the main is more than 3.5 meters away from meter it had to be protected??
so if a flat had a basement with spotlights init and ground floor was the same flat do they need fire protection or is it only when there is a seperate flat above where you are installing the spotlights.
What code would you give if a ceiling rose bulb holder was missing the plastic cover?
and a cable that has been dissconnected from a power shower and left with tape on it??
Distribution Network Operator.
Each DNO has it's own local rules on meter tail length before protection, ranging from 2-5 metres.
Your PIR should only be concerned with BS7671:2008 and not local DNO rules.
Lenny is right about the 16mm though, I missed that in my initial answer, the DNO fuse size is the deciding factor on that one.
The recessed lights are as above, same property/fire compartment then no need to give a defect code.
The last 2, are you talking about a taped up cable in a shower unit? If yes, code 2.
Is it the actual ceiling rose terminal cover that's missing or just the lamp holder skirt?
Code 1 for terminal cover, 2 for skirt.
Is this an inspection that you are actually doing or are these just examples?