PIR codes | on ElectriciansForums

Discuss PIR codes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

J

jimmer

Do all sockets need to be rcd protected on a commercial/shop premises or just ground floor ones? All floors are of the same shop.
Any help much appreciated
 
Hi

BS 7671 411.3.3 socket outlets with a rated current not exceeding 20A that are for use by ordinary persons and are intended for general use require an RCD

It goes on to say an exception us permitted for socket outlets for use under supervision of skilled or instructed persons eg in some commercial or industrial locations or a specific labelled or otherwise suitably identified socket outlet provided for connection of a particular item of equipment

Hope that helps

Chris
 
I agree with Chris & jason..and would suggest Risk assesment to be the deciding factor here.....all installations have their own specific needs.


spark1
 
All socket outlets need to be protected by an RCD unless they are used while under the supervision of a skilled/compentant person. Now I don't know about you but I wouldn't class a 17 year old working on a Saturday to earn some extra cash as a compentant/skilled person nor would I class a manager of a shop as one. They may have first aid training but I wouldn't class this as a competant/skilled person. This kind of person is someone like an engineer who works in a factory and has undertaken the necessary training. But again, like everything in the regs, its all down to you, the installer, to make the decision and personally I would just fit RCD protection. At least your covered!!!
 
Last edited by a moderator:
Well several things, I prefer best practice guide 4 on reccomendation codes, secondly you do not "Fail" an installation doing a PIR it is either satisfactory/unsatisfactory, and I would agree labelling is a 2 ie needing improvement.

Periodics are not for the new electrician, even if you did your 2391 course as part of your training, you need in depth knowledge of the type of installation you are testing.

You also requires a good understanding of the regs and their relationship to installation requirements, so that you are not guessing or misunderstanding those two columns of tick boxes in the schedule of inspection and dozen or so columns in your schedule of test results.

Finally, good as these forums are, you need a process of verification in place so that any grey areas or inaccuracies can be rectified. If you are self employed, send a copy now and then of any certificate to your accrediting body
 

Reply to PIR codes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K
We do have consultancy, but not for such like. The question could be put to the UK property manager, I’m just wondering what you guys have been...
Replies
2
Views
433

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top