PIR done on domestic.
32a ring final circuit with RCD protection. R1 slightly high, most likely due to poor connection (0.92ohms)
R2 ( 0.54).

Does this need coding?

Zs is .53 so no non compliance there, but ob there is a clear fault on the R1.
 
PIR done on domestic.
32a ring final circuit with RCD protection. R1 slightly high, most likely due to poor connection (0.92ohms)
R2 ( 0.54).

Does this need coding?

Zs is .53 so no non compliance there, but ob there is a clear fault on the R1.
Those readings r1 and r2 will be the end to end resistance of the phase conductor and cpc I presume. Did you cross connect and do the R1+R2 tests,
 
Last edited:
A loose connection has the capacity for overheating and/or overloading so I would code it accordingly.
0.54/1.67=0.32 ohms for r1&rn assuming cpc‘s are 1.5mm2 in size.
 
Last edited:
Fails under observation item 5.17.1, as a C2. This is referred to in Best Practice Guide 4 page 14. The tolerance on continuity readings is 5%.
I've seen conductors fall out of the back of sockets when unscrewed, that can still give a reading similar to the one you've found.
It may be worth connecting each leg of the lives in turn at the board, and going round with the plug test lead to see if you can find the offending socket before removing the faceplates.
 
Shouldn't you investigate? Not sure what is entailed within a PIR.

I higher resistance on the r1 compared to r2 would most likely be a loose connection. I had the same situation myself yesterday. r1 was so loose it fell out as I removed the socket.

Btw (little r1 and r2 refer to the end to end resistances respectively, but you know that?)
 
Shouldn't you investigate? Not sure what is entailed within a PIR.

I higher resistance on the r1 compared to r2 would most likely be a loose connection. I had the same situation myself yesterday. r1 was so loose it fell out as I removed the socket.

Btw (little r1 and r2 refer to the end to end resistances respectively, but you know that?)
What type of cable is being used because if it's Twin and earth r2 will be a smaller size, hence a higher resistance than r1 or rn, wont it?
 

Reply to PIR done. high R1 on RFC. does this need a code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top