PIR done on domestic.
32a ring final circuit with RCD protection. R1 slightly high, most likely due to poor connection (0.92ohms)
R2 ( 0.54).
Does this need coding?
Zs is .53 so no non compliance there, but ob there is a clear fault on the R1.