A friend has replaced PIR floodlight at home. The house is wired 16th edition so no RCD on the lighting circuit, which the outdoor light is connected to. Now current regs state,
"5.7.4 Fixed Equipment
Fixed equipment in the garden such as permanent lighting attached to buildings, should be securely erected with all cables buried or securely fixed to permanent structures clear of the ground. All insulated class II equipment is recommended where possible. Outdoor fixed equipment is not required to be protected by an RCD. A disconnection time of 0.4 seconds is required."
His earthing is PME, and the floodlight is out of reach without using a ladder, so I see no reason why an RCD is required. However the manufacturers instructions state the light must be connected to an RCD. It is IP44 rated, and I've seen loads of these in the past, and the instructions have never specified this. However manufacturer's instructions must be adhered to. Why would this manufacturer specify this when most others don't? Are they just being over cautious? I did suggest fitting a RCBO, but the circuit has smoke alarms. I have suggested he removes the light and replaces it with another manufacturer that doesn't specify the use of an RCD to be squeaky clean. After I will test ELI for him. He's not too happy about this. Am I correct in advising him to do this?
"5.7.4 Fixed Equipment
Fixed equipment in the garden such as permanent lighting attached to buildings, should be securely erected with all cables buried or securely fixed to permanent structures clear of the ground. All insulated class II equipment is recommended where possible. Outdoor fixed equipment is not required to be protected by an RCD. A disconnection time of 0.4 seconds is required."
His earthing is PME, and the floodlight is out of reach without using a ladder, so I see no reason why an RCD is required. However the manufacturers instructions state the light must be connected to an RCD. It is IP44 rated, and I've seen loads of these in the past, and the instructions have never specified this. However manufacturer's instructions must be adhered to. Why would this manufacturer specify this when most others don't? Are they just being over cautious? I did suggest fitting a RCBO, but the circuit has smoke alarms. I have suggested he removes the light and replaces it with another manufacturer that doesn't specify the use of an RCD to be squeaky clean. After I will test ELI for him. He's not too happy about this. Am I correct in advising him to do this?