swift colin
Just had a PIR done for a house we were hoping to buy.
The house - victorian/edwardian terrace - has 8 circuits and the wiring is approx 20yrs old according to the PIR.
The report gives the same reading for ALL circuits. Live-Live is 1.01 Mohms and Live-E is 0.17 Mohms. Continuity Polarity and Zs all seem OK. Each circuit having different (R1+R2) values and different Zs values.
I understand that the insulation resistance readings are not good and that further investigation will be required.
Despite reading (IEE books) about the test, the method of performing the test and the acceptable results I am none the wiser as to how 8 separate circuits tested independently can give the same reading.
Can anyone enlighten me as to whether this is possible? or give me some idea of what to ask the electrician who did the test so that I can have a meaningful discussion with him.
When doing an IR test, U can test all circuits at once. If you then get results like yours, you would then go on to test each individual circuit untill you find the one that is not good.
He may have carried out a global test, ie. on the whole installation at the consumer unit tails, and just filled in the same result for each circuit.
With readings this low, I would (although I do this anyway, regardless of a low global reading or not, unless it was above 10Megohms), is to carry out an IR test on each circuit individually, this would have shown up one or perhaps more faults on the individual circuits.
There may also be something still connected, eg. Neons, Alarms, Boiler controller,aerial amplifier etc..., this would give false low readings.
I would ask him how he got the same readings for each circuit, and if it is as above, ask him to re-test properly.
With those readings there is almost certainly equipment connected so they don't really mean much.
There could even be 1 circuit feeding outside equipment with dampness giving the low readings.
Looking at a small piece of a PIR is not going to tell you what questions to ask your electrician. But the readings you have stated would suggest that a global test has been done. GN3 says that any result under 2Meg requires further investigation which is what should have happened. You say Continuity Polarity and Zs all seem OK but what are you compairing against? Each circuit having different (R1+R2) values and different Zs values - you would expect this but on PIRs I would be doing R2 readings
What was your brief for the PIR? PM me if you wish to discuss off the open forum
Back to the OP - what was the outcome of the EICR? Satisfactory? Unsatisfactory? If the later what are the comments and codes.
IMHO the IR readings must be suspect and as others have said they must have been done on a "global" basis which isn't giving you a real picture of the install.
I'm guessing you've paid his bill!
when on a PIR i will hit it first (IR) at the tails...see what i get....if i dont like it (under 10 meg)....then i will do em all individualy.....theres either a connected load here .....or water in a fitting someware....outside maybe..but i think thats already been mentioned here already.....whether the R1 R2 method....or just a plain R2 method is used is neither here nor there.....it would also depend if you had your wander lead with you..(maybe it got left out of the van)..who knows...but........
what should have happened here of course is this `electrician` should have immedietly given this a (3)...but ready to go to a (2)...upon further investigation when the offending circuit/s had been found........which doesn`t appear to have happened here....hmm.....
I wonder how much the OP paid for the EICR? Me thinks it was underpriced and he/she didn't allow sufficient time to do a proper job
well this is it Murdoch.....all easy n well to point out what a naughty `sparky` he was....but lets face it....unrealistic budget+unrealistic timeframe......we get this all the time....and not just on PIRs either.....like the other day we were on a job and after about 1 hour or so of being in there..she came out of the living room askin us `how long will it be`?....this on a job that was expected to last all day.....the client knew this n all......
If individual circuit tests have been carried out for continuity and loop impedance, how much more effort would it have taken to do the same for IR ?:confused:
We are finding Insurance companies are starting to do this as alerted by an irate customer.
Zurich Engineering has been in and tested a Church and Church Hall that we carried out a periodical a few years back and then quite a few remedials were done. Zurich came up with a satisfactory report which had defects requiring remedial action before further use.
All the defects are due to the fact they have not carried out insulation resistance to seperate circuits and has just confused the customer.
A few years ago a mate of mine rang me up as his son had just bought a house had everything checked and electrics came back as fine,however my mate was suspicious and when I went to look even before testing anything I saw old rubber cables all perished going into the CU, an old Wylex with rewireable fuses,no bonding anywhere total mess.the inspection was part of a survey organised by the bank who were doing his mortgage,mates son went spare and asked me to rewire house,rang bank and made appt to see manager,had to laugh turns out he went in and before giving him my report dropped wylex on his desk and asked if he knew what it was,guy said it looked like a fusebox that needed replacing,anyway to cut it short bank refunded full cost of survey and paid for rewire.
Thanks to everyone who left a reply.
Murdoch
£200 +VAT. So I ask a man to do a job. Pay him what he asks and its my fault he didn't do the job because I didn't pay him enough?
Ipf
Not much I suspect. But its even less effort to trouser the money and leave saying more investigation needed.
Can't account for any problems encountered but, for the price, I would have expected individual IR circuit tests. I don't think Murdoch expected such a payment.
Back to the OP, did the PIR give you a satisfactory or unsatisfactory result - if the latter what are the issues listed?
PIR Insulation Resistance Test
swift colin,
Octopus,