Jazza

A friend of mine has had a company do a PIR on there property, must be renting it out or something.

They were told they needed RCD protection on there shower circuit as an urgent requirement.

Is it possible to fit an RCD after the 45a mcb for the shower circuit. The cable is surface mounted with loads of slack and as they dont want to change there old school Consumer Unit.
 
thanks for the reply. Unfortunately it is only surface mounted in the cupboard where the cu is. I put that info in because there is a bit of slack on the cable and an rcd could fit in nice between board and shower.
 
lol, it did seem a little like that, company was gas elec. supplementary bonding is present but cable is not surface mounted the whole way just can see it as the only cable going up the wall. meaning the rest are buried and someone must of added the shower in at a later date.
 
wil the board take a RCBO?
 
the board is an old style wylex, not sure what fittings you call them, but someone has put some ge mcbs like you see on the newer boards.

can you get an rcbo for that
 
as regs changed in 2008!!! if it was existing and it was installed to 16edition then its fine (providing bonding is connected)!

to many people jump on the RCD "save you life cover all scenario"

if a recent addition then 17th would stipulate RCD etc....!!


they have installed push in MCBS!! you CANT get push in RCBO!!


back to original question thoough yes you can install a RCD "After" the Fuse! or why not split the tails and install a Standalone box for shower!!
 
Last edited by a moderator:
because if it was compiant at time of installation, the only needs a code 4 on the PIR
 
ahh I see, I dont think its a recent edition as it is wired in the original red and black. If they still want rcd protection on that circuit, is it ok to put it on the demand side of the circuit, due to the cable being visible?
 
Interested to know what he wrote on the PIR regarding the shower circuit and what code he gave it?
 
probably give it a 1 as never undertaken work done to previous versions at his 1 week training centre!


if im right Gas Elec are a franchise similar to Mr Electric and thus OVERHEADS = THIRST FOR CASH!!

no RCD = EASY MONEY!!
 
Last edited by a moderator:
it wasnt like a proper PIR form he had, it looked like one generated by them. gas elec i think they are called. it just had written down under observations that the shower circuit needed an RCD urgently
 
can anyone direct me to the specific reg that says prior to 2008 installations do not have to meet current standards
 
By what you've said jazza it is within the regs but if the home owner is concerned about it just install a stand alone rcd unit next to the c/u as said above. Reading in-between the lines and coming up with my own thoughts, this is a company trying to threaten them into opening their wallets. I'd be rich if I had the same scumy levels that they have.
 
can anyone direct me to the specific reg that says prior to 2008 installations do not have to meet current standards
there was no BS7671(2008) when it was installed.so how could it comply with a non existent regulation?
 
Just had a look at the 16th OSG. Shower in zone 1 must be ipx4. Any other appliance (other than heaters, showers, pumps) must be on a rcd. Seen as its old colours that's before 2008 I think that's all you need.
 
If installed correctly, using the correct cable CSA rating, correctly rated protective device, and the cable is installed correctly then this would only warrant a code 4 on a legitimate PIR, meaning it does not meet current regs on having no RCD protection. There is no immediate danger here.

If he's noted the shower should have RCD protection then why has he not noted it for the lighting in the bathroom?

Because it's not required to get a satisfactory on a PIR, that's why..

How do these firms get away with this scare tactic?? I'll bet we'll be seeing them on rouge traders soon..
 
Gas Elec eh mm is it one of their land lords certs as they call them ,there was a guy round here doing inspection for gas elec ,no 2391 no 17 edition but he's doing inspections , as the guys have said if its up to 16th edition with a sup bond to the light as well and sup bonding in place then there not a problem with it and the coding should be code 4 does not comply with BS7671 2008 (satisfactory)as we now do periodics to the current regs
 
Personally I believe 2 (Requires improvement) is more appropriate than 4.

Just because the 16th Edition did not state that all circuits in a location containing a bath or shower required 30mA RCD protection does not mean that you cannot in your judgement suggest that improvement is advisable.
 
Although it is the opinion of the inspector as to what code is warrented by any situation.
I believe that he would have a hard time justifying any code in this instance, considering as the guidance given by the ESC and the Part P schemes is that this doesn't warrent a code.
 
Personally I believe 2 (Requires improvement) is more appropriate than 4.

Just because the 16th Edition did not state that all circuits in a location containing a bath or shower required 30mA RCD protection does not mean that you cannot in your judgement suggest that improvement is advisable.

But if supp bonding is adequate and present why would it require improvement?
 
just before the 17th edition came out i was at a seminar by the nic my answer was what they advised , when i carry out a periodic im testing to the current regulations and although the installation is up to 16th edition standards its not up to 17th edition standard so realy the only code for it is a code 4 , with a reccomendation for an upgrade ,
 
Loads of 5 week wonders (guys who only have experiance of 17th0 seem to put "No RCD" on forms to cover their own backsides but code wrongly
 
Are we not overlooking the requirements of the manufacturer, you'll find manufacturers were requiring rcds before the 17th

Chris

True. However in a PIR you may not have the instructions on hand that state this, therefore the regs would be your first point of call. If you had the instructions, suppose thata another way of looking at it.
 
If the manufacture's installation instructions were not available, to determine whether an RCD was required, would that not involve further investigation?
Would not a code 3 be more applicable?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
PIR "no RCD on shower circuit"
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
34

Advert

Thread statistics

Created
Jazza,
Last reply from
Deleted member 26818,
Replies
34
Views
13,621

Advert

Back
Top