A

aaelectric

Hi went to do a periodic report today on a property and found the following observations.I know the current recommended codes but what about the new c1 c2 c3.Main armoured from meter more than 3 meters with no isolator/fuseNo RCD protection on bedroom sockets or breakfast bar No blanks on fuse board No danger signsFuse board marked incorrectlyMain earthing terminal not fixed, hanging loose Although kitchen and outside socket have RCBO installed they didn't install on bedroom sockets, appliances smoke alarms and lighting. Most circuits at some point will be buried less than 50mm in walls etcWould you put rcbos for the lot?Wiring looks within 4-5 years oldWould you say isolator for main is to be provided by network provider.Also would you still use the old reports or is it law now we have to use the EICR Thanks
 
Hi went to do a periodic report today on a property and found the following observations.I know the current recommended codes but what about the new c1 c2 c3.
Main armoured from meter more than 3 meters with no isolator/fuse C2
No RCD protection on bedroom sockets or breakfast bar C3
No blanks on fuse board C1
No danger signs C3
Fuse board marked incorrectly C3
Main earthing terminal not fixed, hanging loose C3
Although kitchen and outside socket have RCBO installed they didn't install on bedroom sockets, appliances smoke alarms and lighting. C3
Most circuits at some point will be buried less than 50mm in walls etcWould you put rcbos for the lot? Not relevant to EICR
Wiring looks within 4-5 years old
Would you say isolator for main is to be provided by network provider. No
Also would you still use the old reports or is it law now we have to use the EICR All work done should be to the current regulations so should use EICR not PIR, but not law, guidance.
Thanks
These are my thoughts on coding and actions.
If you have already done a PIR then you may have problems translating to EICR!
Sounds like a bad initial install must have just beaten 17th.
 
I would also concur, except I would advice a C3 for the lack of RCD protection for the cables concealed in walls at a depth less than 50mm.
Yes I would rather use RCBOs than an RCD covering multiple circuits.
 

Reply to PIR Or EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
832
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
930

Similar threads

This fella puts his face to it about halfway through, he has an opinion on the very subject.
Replies
42
Views
4K
The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top