Hi everyone in advance, carried out a PIR today, nothing special 8 circuits on a dual rcd board, supply is TN-S. Done a Ze at service head and got 0.10 ohms (very good i thought). However here is my problem, the radial for the boiler and the ring circuits came out at 0.90 approximately. R1+R2 are 0.23 approximately and length of run is about 15-20 metres.

It has a crabtree starbreaker board ( with the enclosed busbar) has anyone else had high readings when testing or is it just me.

Checked all screws for tightness and were all ok, even checked all sockets. Couldn't find anything obvious

Thanks in advance

Chris
 
a bit of an effect caused by the MCBs, esp if you are using the no-trip loop test. as long as the readings are below the permitted max. ( which at 0.9 ohms is , for a 32A type b and all lesser rated MCBs). job's sound.
 
alternatively you could derive Zs from Zs= Ze+ ( R1+R2 ). your continuity readings look spot on. (a 10m radial in 2.5/1.5 should give around 0.2ohms.)
 

Reply to PIR today in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
889

Similar threads

That is very cool. It would be the end user software that would make that the absolute king.
    • Winner
    • Like
    • Informative
Replies
1
Views
468
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top