now im doing a pir on a large old building now because there are so many additions there are loads of plastic speed fit joints on copper pipe work now i am putting this down as not acceptable because there is no continuity on the pipe work.<BR><BR>am i right in saying this as it has never been picked up in the last report the installatin was acceptable<BR><BR>i dont want them thinling im making it up for more work im just doing my job.<BR><BR><BR>what would u do ?<BR><BR>thanks
 
Hi, I thought that the provision of an RCD was used in order to overcome this? I think you can get around it if you RCD protect the installation, although I dont have my BRB to hand to assist with a reg.
 
The main bond to services water etc is at the incomming supply ,this stop any potential faults comming into the building from the outside , if the pipes have been insulated from the main earth by these joints then there is no problem supplimentary bonding can be omited when RCD protection is provided to all circuits and providing certain criteria has been met
 
ok but what if there is a fault to a ac unit or boiler or a bit of equiptment which is plumbed in or a ice machine or a cable melts over the copper pipe it will just be live and not blow a fuse or anything also how would a rcd work if there is no continuity in the pipe and it can happen.
and it is a large building with about 200 circuits so a rcd is not going to happen
 
If there is a fault on a piece of equipment I would hope that it never relied on bonding to disconnect the fault to be honest. Earth limits the fault duration, and bonding limits the touch voltage. So for a class I piece of equipment I would hope that your CPC would carry away the fault and if the circuit is designed correctly then it will trip the device.

You can check these pipes to actually see if they are extraneous conductive parts. Also you only need to fit suplementary bonding in a special location ie a room containing a bath or shower.
 
main earthing will limit the duration of a fault and main bonding limit the magnitude.

any leakage to earth would cause a imbalance in the rcd causing it to operate, bonding the services will allows metalwork to rise to same potential under fault conditions.


Malc types quicker than me :)

where a mixture of plastic and copper pipework is used in a building main bonding should still be carried out at incoming services position, where the intake and complete installation is all plastic then main bonding may be ommited.
 
Last edited by a moderator:

Reply to plastic pipe fittings in the Australia area at ElectriciansForums.net

Similar Threads

Sorry for the late response but by the NEC code book requires one ground rod near the panel and another ground rod at least 6 feet or more using #...
Replies
1
Views
826
  • Question
You do both, "fix the problem" even if it is only there in the eyes of one person. send an invoice for the extra work needed to raise it from...
Replies
14
Views
2K
  • Question
Nothing wrong with it. Which manufacturers have you got this information from? What do you mean by trip speed? Fuses and MCBs can operate in the...
Replies
11
Views
1K
davesparks
D
  • Question
I don't think there is a conspiracy here .. but I do think 5he sort of loadings we are talking about with things like electric boilers and single...
Replies
24
Views
3K
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
820

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks