View the thread, titled "Please Explain: Symmetrical fault current" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.
daveede
Im doing my 2391 course and it was quickly mentioned about symmetrical fault current when talking about PFC testing.
It was just mentioned and not explained so can anyone explain what this means.
My first thought is that 3 phases shorted together would cancel out and leave 0 volts??
But this cant be correct or cant be the whole story as its must still produce a fault current or it wouldn't be in the course.
I have tried to google it but not really getting anywhere cant find the answer and what i am finding is just crazy looking math and talking about transformers and motors
Thanks for the help guys
A symmetrical fault is a fault that affects all phases in an equal fashion.
An asymmetrical fault is a fault that only affects say 2 phases of a 3-phase system.
The prospective short circuit current line to line will be 1.732 X the line to neutral value in a 'text book' 3-phase/N installation.
As a 'rule of thumb' Guidance Note 3 recommends multiplying the measured line to neutral prospective short circuit current by 2 to obtain a line to line value that errs on the side of caution.
very good indeed IQ
what I dont like is GN3 note to double pfc, I always record pfc x 1.732
Thanks for the replies
The bit im wondering about is if you short all 3 phases wouldn't the sine wave cancel to zero, and if this is correct how do you get a fault current. i guess you get a fault if the phases weren't balanced somehow but this would seem to be small at first thought because they would have to be pretty unbalanced to make a large fault almost like only 2 phases shorted etc
ps. This may be why the pages i googled were talking about motors and transformers, is it anything to do with voltage and current being out of phase
doubling can cause more problems than what it is worth, especially if you have a Ze of 0.01 and fuses that can only handle 40 Ka fault current
If you picture the timing of the 3 phases P1, P2, P3 (that's the implied sequence). When P2 is at it's peak, where would P1 and P3 be in their cycle?
hey topquark,
Thats pretty much what i mean, across 2 wires or across a load the difference is the peak of the sine wave gives you the potential / voltage.
But 3 phases in 1 wire would sum to zero as in your example if:
L2 is at peak
L1 is rising from its negative peak
L3 is going towards it negative peak
So its all the 3 waves are added as in 1 wire they would cancel to zero potential
If i remember correctly for sine graphs for non electrical you would calculate the area under the waves and they would be equal and therefore cancel, assuming this works for electrical aswell.
For that single wire with all phases yep. However we only ever considering two phases with respect to each other for fault potential. You are always looking at the worst possible fault scenario.
So yes you are correct (and so is the maths).
You can probably visualise that easier if you look at the timing for L2 half way through it's cycle, then L1 and L3 are at opposite peaks.
Thanks for the reply
What does this mean in terms of Symmetrical fault current which i believe is all 3 phases shorted, so how do you get a fault current etc
2 phase pscc is ok i get that no probs
Maybe i just need to know where the fault current in Symmetrical fault current comes from / goes to, or is it just an exchange between all 3 phases but wouldn't ever go to earth or neutral
That would depend on the nature of the fault, consider an over voltage fault affecting all 3 phases. You are still then considering the fault between two phases as the highest PD and hence current.
I think, what may be confusing here is that with a symmetrical fault you are not considering all three phases for what current could flow, still only two. The nature of the fault itself is still symmetrical, in that it affects all 3 phases.
Reply to the thread, titled "Please Explain: Symmetrical fault current" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.