The pump motor may have an internal thermistor protection that can be wired back to a relay or DOL starter, this is the best type of protection and most likely to detect issues before damage occurs. If not, the type of manual motor starter you have in the photo would be fine to provide adequate pump protection except it requires a lower current range so it'll have to be replaced.
The circuit breakers (MCB's) protect the installation wiring, not the pump itself, so they should be sized according to the wiring sizes and C or D curve are okay if they can meet disconnect time requirements on that particular circuit. If this is a pool pump then an RCD would be appropriate for the pump but I doubt you'll find a 3mA RCD, a 30mA would be considerably cheaper and fine. The lighting should be fed from an isolating transformer so an RCD shouldn't be necessary for the lights.