We had a electrical panel made of Mild Steel which contains Starters rated 3-phase 440v and control circuit voltage of 230V taken from a phase and neutral. The problem is that, while testing the panel we are getting a voltage of 230V between a phase and body. The body is not earthed. There is no contact between neutral and body anywhere. When Meggar test is done, we got a resistance of 100 ohms. Why is this so? What would be the reasons for this to happen?
 
What is the body mounted to? Have you tried testing between the body and earth?
 
To read any voltage you must have your meter connected to two points at different electrical potentials. If you are getting a reading the body must be making some contact with earth, possibly through the mouting fasteners and the surface on which it is mounted. Your megger reading of 100 ohms indicates that the body does indeed have some sort of connection to earth. If not, the reading would be in the high megohm range. If the body was fully insulated from earth your volt meter would read zero,
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Please solve our Problem
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
pssdeepak,
Last reply from
gordonjt,
Replies
3
Views
1,032

Advert

Back
Top