paul11

The heater was plugged into a double socket. Which was on its own 16amp radial.

after a few months of use the socket was not working.

i get a call so I straight away put plug my socket tester in.

its saying there is no neutral connection.

the client hen says she plugged the heater into a diff socket. I checked that and I had the same problem.

Both socket were damaged where the netruel prong goes.

i think it's a faulty heater, but could it be any thing else.
 
Loose Neutral in the Plug causing too much heat, Is the cable damaged or is the fault with the actual socket ?
 
No cable damage just at the socket.

would never no if it was a faulty n in the plug, as you carny get in to the ****
 
heat has transferred through via the metalwork of the plug pin to the wall socket plate and baked its insides......renew the two sockets, chop off the plug on the heater and replace with a new plug.....jobs a goodun :)
 
The heater was plugged into a double socket. Which was on its own 16amp radial.

after a few months of use the socket was not working.

i get a call so I straight away put plug my socket tester in.

its saying there is no neutral connection.

the client hen says she plugged the heater into a diff socket. I checked that and I had the same problem.

Both socket were damaged where the netruel prong goes.

i think it's a faulty heater, but could it be any thing else.
I wouldn't take a hens word for it their brains are tiny:D probably a loose neutral in the plug or the heater
 
No cable damage just at the socket.

would never no if it was a faulty n in the plug, as you carny get in to the ****

Moulded plug!? then cut it off and replace with a plug you can check

The best moulded plug is the one that's in the bin IMO they are useless on high low appliances
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Plug in electrical heater 3kw
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
paul11,
Last reply from
Engineer54,
Replies
7
Views
1,775

Advert

Back
Top