Plumber changes boiler and RCD main switch starts tripping at various times when its firing up or soon after. (I was there doing other work).
I test ring (that its connected to) and get +299Mohms on all tests. RCD doesn't trip at x0.5 and trips at x1 and x5, all fine.
I've suggested to them that the boiler must be faulty.
Customer has since messaged me saying plumber says its tripping as consumer unit needs changing as it's and older consumer unit and RCD is not compatible with the boiler.
I've since finished my works and asked customer if it's still tripping.
"No but they had to put an older model of pump in... Something about the ERP pump and earth leakage. Apparently only certain breakers cause it to trip, most are fine but our current one isn't. (I hope that makes sense as I have no idea what it means)"
The plumber has his own spark who
he called for advice while I was there. I was sure it is a get out excuse and they have 'saved face ' with that excuse and at the same time putting the old non faulty pump back on.
I'm getting a board change out of it but for my own peace of mind, is there something special about a new pump or is it simply faulty with +30ma leakage.
I didn't do a ramp test with loads connected but at x0.5 with loads connected it did not trip (I know loads should be disconnected but I tested from a local socket).
Thank you
Every day is a school day, so happy to be
I test ring (that its connected to) and get +299Mohms on all tests. RCD doesn't trip at x0.5 and trips at x1 and x5, all fine.
I've suggested to them that the boiler must be faulty.
Customer has since messaged me saying plumber says its tripping as consumer unit needs changing as it's and older consumer unit and RCD is not compatible with the boiler.
I've since finished my works and asked customer if it's still tripping.
"No but they had to put an older model of pump in... Something about the ERP pump and earth leakage. Apparently only certain breakers cause it to trip, most are fine but our current one isn't. (I hope that makes sense as I have no idea what it means)"
The plumber has his own spark who
he called for advice while I was there. I was sure it is a get out excuse and they have 'saved face ' with that excuse and at the same time putting the old non faulty pump back on.
I'm getting a board change out of it but for my own peace of mind, is there something special about a new pump or is it simply faulty with +30ma leakage.
I didn't do a ramp test with loads connected but at x0.5 with loads connected it did not trip (I know loads should be disconnected but I tested from a local socket).
Thank you
Every day is a school day, so happy to be