Hi,
ive been tasked with writing a 'standard operation sheet' for plumbers to replace electric showers safely.
at the moment they are replacing showers with no test gear, then the electrician is following behind doing a Zs
my concern is; they turn it off at the dp switch and remove the shower, I am not happy that it is dead when they turn if off as they have no method of checking. There may be a fault on the dp switch and they would not know
is this an acceptable procedure
remove cover of shower.
turn shower on by double pole switch,
VOLTSTICK (yes I know) will indicate,
if volt stick does NOT indicate, stop and wait for advice off an electrician
turn off by dp switch, VOLTSTICK will stop indicating,
if VOLTSTICK does not stop indicating, stop and wait for electrician
switch breaker off at board and proceed
i know what you are going to say, but the company won't pay for test gear for 20+ plumbers, hence the VOLTSTICK idea.
is this classed as safe enough, it's safer than what's happening now,
cheers
ive been tasked with writing a 'standard operation sheet' for plumbers to replace electric showers safely.
at the moment they are replacing showers with no test gear, then the electrician is following behind doing a Zs
my concern is; they turn it off at the dp switch and remove the shower, I am not happy that it is dead when they turn if off as they have no method of checking. There may be a fault on the dp switch and they would not know
is this an acceptable procedure
remove cover of shower.
turn shower on by double pole switch,
VOLTSTICK (yes I know) will indicate,
if volt stick does NOT indicate, stop and wait for advice off an electrician
turn off by dp switch, VOLTSTICK will stop indicating,
if VOLTSTICK does not stop indicating, stop and wait for electrician
switch breaker off at board and proceed
i know what you are going to say, but the company won't pay for test gear for 20+ plumbers, hence the VOLTSTICK idea.
is this classed as safe enough, it's safer than what's happening now,
cheers