D

delindevon

Hi all,
I have just been to price a CU change. The problem is the CU is about 20m from the mains position and is run in 16mm T&E. Here's the good bit the 16mm runs through a neighbours flat, so it can not be replaced and I can not run an earth next to it. I can, though not easily, run another earth and a stake. If I do I think I should disconnect the PME, although I dont want to. What about a RCD to protect the 16mm if I fit one I can't seperate the circuits inside the flat and a RCD 20m away is not ideal.
Any ideas, thanks Del.
 
Last edited by a moderator:
one you do not disconnect a PME system if the cu is about 20 meter from the mains position you need to install a seperate db with a 63 amp mcb ,then change the cu as normal with a 17th edition ,as for the 16mm in a neighbours flat this needs to be relocated , on a PME TNCS installation then the max Ze is 0.35 , once you have installed the 16 mm check the Zs the max for a 5 sec disconnection time is 0.73 you should be able to reach the max ZS for the other circuits if this cannot be reached add an additional earth , and dont forget the bonding to water gas etc this has to be installed at the point of entry of the service and then to the mains incomming DB
 
as for the 16mm in a neighbours flat this needs to be relocated
That's the nub of the problem I can't run a new cable, the neighbours flat is between this flat and the mains position. The cable will have to go through or around the neighbours flat neither of which is an option.
 
is the mains supplying all the flats,if so this should be installed with an isolator so all the flats can be isolated with one switch , the only thing i can then suggest that the dist board in the neighbours flat is labled warning of the supply form your flat , as you can imagin giving advise is difficult with out seeing the installation or more info
 
Nick, all the flats have seperate meters and a switch fuse each in the meter room. The problem is the size of the earth,and the fact that the 16mm is not protected by an RCD. I can measure the run properly I think it's more like 10m to be honest.
 
the biggest problem is protecting the 16mm as if it trips you loose the whole supply , 16mm twe has a 10mm earth , i know the installed size should be 16mm but if all the Zs readings can be met then there shouldnt be a problem ,its also on a switch fuse so the cable is protected ,if the cable is more than 50mm from the surface or installed in a position where it cant get damaged then its fine , where its exposed you could installit in a earthed steel trunking then it will not need RCD protection
 
Thanks for your input Nick, it's nice to get other peoples ideas.
The big problem here is that short of buying the next door flat I can not move check or alter the 16mm. If there were no regulations and presuming the Zs is OK I would fit a 100 m/A RCD at the mains position and 30 m/A RCBO,s in the flat, there is only 4 circuits, then Robert would indeed be your Fathers brother. Alas its not as easy as that. I have wondered if I were to put a 30 m/A RCD at the mains position then disconect the earth when it gets to the flat and fit a stake for the flat would that cover the regs. An earth fault in the flat would not trip the mains position RCD but the 16mm would be covered. Its odd and I dont like though as it would mean 2 earthing systems, all be it seperate on the same instalation. Is there another way?
 
from what I have read it is the kind of job I would walk away from unless you can get the full co-operation of the other flat owner in order to do the work correctly. Is it worth the hassle for £300 max? !
 
I dont mean to split hairs but 16mm T&E has a 6mm CPC which may have a bearing on any calcs he might do.

I noticed that Lenny but you beat me to it.

Where do we find a reference guide to number of strands and csa of each strand in cpc's ? Are the number of strands and csa the same in a bare cpc in a T&E as they would be in a stand alone Earth cable..Just wondering
 

Reply to PME and earth stake? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

  • Question
To give you some idea....with my DNO, the question "Can you see arcing, sparking or smoking?" is 3.5 minutes into the automated call answering...
Replies
8
Views
695
It's not uncommon to find the earth cable put out from the additional neutral knockout, not the designed one on the side. If the rest of it looks...
Replies
2
Views
903

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top