Just checked the L-N loop at a fusebox and got a reading of 0.12ohms (great! ), so going to call up and try to arrange to get a PME system put in. Anyway I was just going though 5.4 regs and didn't spot where (assuming it's in there) it says if it's ok to have both PME and TT earth connections (going to the same CU), anyone else familiar with this or found it in the big book?
Basically do I need to get rid of the connection to that earth rod, or just hide it while the guy is on site to install the PME?
Little background on the place: it's currently got a whooping 800 odd (something up there, why count rotten eggs?) earth reading on a TT that as far as I can tell is a rod buried in mostly builders rubble. Sure that's still well under the 1667ohm mark, but of course there's no rcd in there and 850ohms on an rcd is still rubbish. The ground is so bad putting more rods in would be like throwing **** at a fan, long back-breaking ****s at a hard dry fan.
Basically do I need to get rid of the connection to that earth rod, or just hide it while the guy is on site to install the PME?
Little background on the place: it's currently got a whooping 800 odd (something up there, why count rotten eggs?) earth reading on a TT that as far as I can tell is a rod buried in mostly builders rubble. Sure that's still well under the 1667ohm mark, but of course there's no rcd in there and 850ohms on an rcd is still rubbish. The ground is so bad putting more rods in would be like throwing **** at a fan, long back-breaking ****s at a hard dry fan.