just been to have a look at some electrical work on a house, underneath the main fuse there is a trafolite label saying PME system but the supply authority haven't supplied an earth, someone has clipped a 6mm cable down the side of the house and buried the end in the ground (stripped a foot of the end of the cable) ze is 300 ohms.

do i just need to get onto the supplier to provide an earth and if so why wasn't one provided in the first place
 
PME is protective multiple earth ,TNCS today the earth and neutral are connected at the suppliers cut out , on the side of the supplier cut out there should be an earthing block the earth should be conneted there
 
there is an earth block, the only earth going to it is from under the floor outside, the supplier has not provided an earth, should i tell the customer to get onto the suppliers
 
Isolate supply and disconnect 6mm cable out of earth block test Ze at earth block (not cable) if you get a reading of less than 0.35 ohms then you have a TNC-S. If this is the case you can connect into the earth block without involving the supplier.

You stated you had a Ze of over 300 ohms i take it this was an Ra reading on the cable.
 

Reply to pme earthing in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
933
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
To give you some idea....with my DNO, the question "Can you see arcing, sparking or smoking?" is 3.5 minutes into the automated call answering...
Replies
8
Views
733
  • Question
Thanks for that guys I was more thinking about difference in potential between the tub and wet paving flags . The tub is plastic . But it’s the...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top