Need a little advice on this one.

I rewired a house last year, all sorted and signed off, but I was told I would be coming back as there was a new extension planned. Unfortunately the building contractor would only use their own electrician so I lost the extension work, no worries. The customer has put lots of other people my way so he's worth his weight. He asked me just to cast an eye over the electrical work, and certificate as he wasn't one hundred percent with the finished job. Its not the tidiest job but it ok, except.

The main cut out had to be moved by the supplier to a new meter cabinet on an outside wall. The csu was then reconnected via a switch fuse using three core 16mm swa cable. The 16mm line and neutral obviously go straight into the csu. The earth cable runs to a main earth terminal block, but then steps down to 10mm before entering the csu.

This was done, according to the certificate, to satisfy 542.3.1, earthing conductor sized in relation to the neutral as its PME. I've not seen this done before, is it sized properly seeing as for most of its run the earth conductor is 16mm, the same as the line and neutral, all but for the last 500mm?

Cheers.
 
Need a little advice on this one.

I rewired a house last year, all sorted and signed off, but I was told I would be coming back as there was a new extension planned. Unfortunately the building contractor would only use their own electrician so I lost the extension work, no worries. The customer has put lots of other people my way so he's worth his weight. He asked me just to cast an eye over the electrical work, and certificate as he wasn't one hundred percent with the finished job. Its not the tidiest job but it ok, except.

The main cut out had to be moved by the supplier to a new meter cabinet on an outside wall. The csu was then reconnected via a switch fuse using three core 16mm swa cable. The 16mm line and neutral obviously go straight into the csu. The earth cable runs to a main earth terminal block, but then steps down to 10mm before entering the csu.

This was done, according to the certificate, to satisfy 542.3.1, earthing conductor sized in relation to the neutral as its PME. I've not seen this done before, is it sized properly seeing as for most of its run the earth conductor is 16mm, the same as the line and neutral, all but for the last 500mm?

Cheers.

More like it , that his length of 16mm earth cable was short, and had a bit of 10mm single in the van, which means there will be a joint in the line (hopefully crimp a joint). ...No-one reduces a cable run size, along the way, and least not for the sake of half a metre!! ...lol!!!!
 
Technically they have wired it to the regulations and table 54.8 and so less than 35mm tails is 10mm. I would say if you did the adiabatic equation you could check to make sure that 10mm is fine, but I'm sure it would be.

Remember that it's not 'tails' size that you are using for PME but the SUPPLIERS neutral conductor.

Stick with 54.8 as Malcolm says and you can't really go wrong.

The On-Site Guide is 'idiot proof' in many cases and sticking to BS7671:2008 can often save you a few quid while still being fully compliant.
 
Remember that it's not 'tails' size that you are using for PME but the SUPPLIERS neutral conductor.

Stick with 54.8 as Malcolm says and you can't really go wrong.

The On-Site Guide is 'idiot proof' in many cases and sticking to BS7671:2008 can often save you a few quid while still being fully compliant.

Quite right mate it is the Suppliers Neutral conductor on the main cable, but as I'm not the type to open the head to check the neutral size, I wrongly I agree, just look at the tails coming out of the head to the meter. ...........
 
Last edited:
Ok thanks everyone but I don't think I quite explained it enough. What I was saying is, according to what's written on the certificate, the main earthing conductor, NOT THE BONDING, has been reduced in size to comply with regulations.

I was confused by this but thought there may be something I was missing.

What I think has happened is that the electrician who did the job has confused bonding conductor sizing, with earthing conductor sizing for PME. He must have thought that the earthing conductor had to be sized to the neutral, and so has reduced it to 10mm?

It does still comply. I just thought someone was quoting a reg that I had never heard of.
 
Did you read 542.3.1 for a PME system you do size the main earth conductor to regulation 544.1.1 which deasl with bonding conductors.

544.1.1 tells us PME bonding conductors except for highway power and street furniture must be sized to table 54.8 and for a domestic situation the chances are it will be 10mm as the supply conductor from the DNO will have a neutral smaller than 35mm

So your bonding conductor will be 10mm so will your earthing conductor.
 
Did you read 542.3.1 for a PME system you do size the main earth conductor to regulation 544.1.1 which deasl with bonding conductors. 544.1.1 tells us PME bonding conductors except for highway power and street furniture must be sized to table 54.8 and for a domestic situation the chances are it will be 10mm as the supply conductor from the DNO will have a neutral smaller than 35mm

So your bonding conductor will be 10mm so will your earthing conductor.

Exactly, I had this discussion on another thread last week but I think I failed to convince!
 

Reply to PME protective conductor sizing? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

Nope no fuse or MCB located anywhere apart from of course the 100A main head. I would assume they’ve used the rotary isolator just as a means to...
Replies
6
Views
324
A lot of external bonding or earth conductors are bare copper strips. If mechanical damage is likely, then run some steel conduit… but all UV...
Replies
3
Views
1K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top