That may satisfy the conditions, but you need to be careful here where PME applies, that bond garage MET to Annexe MET may need to be as large as 35mm ! if it is to satisfy both bonding and protective functions.
IN GN8 showing a similar scenario they show 35mm local bonding too.
The Bonding conductors are sized against the incoming Neutral (to the garage) not the supply cable to the annexe, be careful.
Were talking about a granny flat and a garage here not an installation such as is shown the GN8, which is clearly showing 120mm tails. This illustration is basically referring to substantial buildings (commercial/industrial), rather than domestic arrangements...
Taking it that the garage supply is a sub-main from the main house, and the granny flat a sub-main off the garage CU. So the main earth conductor to the granny flat will be identical to that provided for the sub main to the garage CU. Any bonding to services within the garage and granny flat will be the nominal 10mm. Let's hope the sub-main supply from the house to the garage, is suitable to also carry the max demand load of the granny flat!! lol!!