That may satisfy the conditions, but you need to be careful here where PME applies, that bond garage MET to Annexe MET may need to be as large as 35mm ! if it is to satisfy both bonding and protective functions.

IN GN8 showing a similar scenario they show 35mm local bonding too.

The Bonding conductors are sized against the incoming Neutral (to the garage) not the supply cable to the annexe, be careful.

Were talking about a granny flat and a garage here not an installation such as is shown the GN8, which is clearly showing 120mm tails. This illustration is basically referring to substantial buildings (commercial/industrial), rather than domestic arrangements...

Taking it that the garage supply is a sub-main from the main house, and the granny flat a sub-main off the garage CU. So the main earth conductor to the granny flat will be identical to that provided for the sub main to the garage CU. Any bonding to services within the garage and granny flat will be the nominal 10mm. Let's hope the sub-main supply from the house to the garage, is suitable to also carry the max demand load of the granny flat!! lol!!
 
What I was pointing out E54,

Were talking about a granny flat and a garage here not an installation such as is shown the GN8, which is clearly showing 120mm tails. This illustration is basically referring to substantial buildings (commercial/industrial), rather than domestic arrangements...

Was that the bonding conductor has to be sized to the DNO's incoming Neutral at the supply to the garage (the OP's actual supply source), not the Neutral that supplies the granny flat.

It may well be the case that 16mm will be ok, in parallel with the incoming Earth csa and armourings, I did say it may have to be larger if it was combined as the protective conductor as well as the bonding conductor (that may, or may not be the case here) .

As I cannot see the install, and don't know how it is supplied (armoured ?, T&E ?), I only advised caution wrt sizing.

The Picture shows the bonding is sized to the PME incoming supply Neutral.

Cheer S68

Edit: if the OP's supply is fed with armoured cable with a separate CPC core, it may have a large enough CSA t satisfy the conditions required without needing a separate bond back to the supply MET, which I also said earlier in the thread. :wink_smile:, but I don't know for definite if this is the case.
 
Last edited:
That's what i was pointing out, you only need 10mm bonding conductors for up to 35mm incoming supply conductors. You'll rarely if ever, see larger than 35mm on a domestic installation.
 
That's what i was pointing out, you only need 10mm bonding conductors for up to 35mm incoming supply conductors. You'll rarely if ever, see larger than 35mm on a domestic installation.

True, assuming the garage is a domestic type, in the OP it just said it was a garage and workshop (with it's own supply), which again I don't know the details of, and it could be anything, so I did not want to say just do X and Y, in case I was giving false information.

Anyway I did better than Napit technical lol , who did not want to commit. :wink_smile:
 
Morning. Garage is a domestic double but has its own 100 A PME supply. No load to speak of on it ( 1 florrie and 2 dbls via an 8 way 100 A main switch split load 63 A 30 mA RCD. Annexe has been fed from a spare way on above db via 40 A MCB (Type B ) on a 10 mm armoured 3 core ( armour and 10 mm core for earth)
 
True, assuming the garage is a domestic type, in the OP it just said it was a garage and workshop (with it's own supply), which again I don't know the details of, and it could be anything, so I did not want to say just do X and Y, in case I was giving false information.

Anyway I did better than Napit technical lol , who did not want to commit. :wink_smile:

You did indeed!! lol!!!

It seems we both assumed wrong, but then who would have ever guessed that a domestic garage would be on it's own metered PME supply!! lol!! Wonder how long this owner has been paying 2 electric bills, or maybe it was brought in recently, specifically for the annexe granny flat because it was easier to route the cable, than supply the granny flat direct!!?? Who knows!! ...lol!!

Anyway, he still only need to bond the gas service pipe were it enters the separate annexe, no need whatsoever to link the two MET's from the two separate supplies. It's the same situation as you would have in a block of flats, bonding wise...
 
Last edited by a moderator:
I believe originally there were a lot of old sheds behind the garage which were going to be let as small units for cottage industries so the supply was brought into the garage for them. Guess this never happened and so he thought use it as its there. Still think it would have been easier to have put new ccts onto existing house db. Saved a lot of SWA IMO. would the gas pipe bonded at each end to different PME supplies suffice ?
 
I believe originally there were a lot of old sheds behind the garage which were going to be let as small units for cottage industries so the supply was brought into the garage for them. Guess this never happened and so he thought use it as its there. Still think it would have been easier to have put new ccts onto existing house db. Saved a lot of SWA IMO. would the gas pipe bonded at each end to different PME supplies suffice ?

It'll be the same DNO's PME supply, maybe on different phases from the same network cable though!! Yes it will suffice, as i say no it's different to a block of flats, or even a row of houses that each bond to a common service pipe as it enters the property... No need to over think or complicate matters here!!
 
Haha I've been told before about over thinking !! Thanks very much for your helpful advice. Think I will on this occasion let the plumber finish what he started and contact LABC himself. Useful info all round
 

Reply to Pme query in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

Your kWh figures are giving you consumption averaged over each hour period, but don't give an indication of total instantaneous current. To try...
Replies
9
Views
1K
D
  • Article
DHW supply from Vaillant turbomax 828e Hi, We have a combi boiler supplying dhw and c/h to our 4 bed, 2 bath house. The boiler is in a cupboard...
Replies
0
Views
139
diddlepara
D

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top