davesparks
It’s a very large installation with its own substation clearly labelled PME. Also the installers who fitted the Distribution board have noted it as PME.
If it has its own dedicated feed from a substation then it can't be PME. For a supply to be PME there needs to be multiple N-E connections along a distributing main, it's not possible to achieve that multi earthing on a dedicated feed.