A

amicus

HI Anyone know definate rule on feeding garage from house on pme?I see so many opinions im not sure anymore.Briefly i intend to run a 6mm 3core swa to rcd garage unit,fed from 30a mcb in house.Approx 25m run,and no other services or metal entering garage. Is this ok or are we in earth rod territory.Thanks.
 
I believe it's mentioned in the electricity supply regulations. ( sorry for lack of detail wasn't 100% sure myself whether it was mention in there)
 
Last edited by a moderator:
It is, but, as you say, there are no other services in the garage so there is no reason why not.

However, i always split the earth out at the garage and bang a rod in the ground regardless.
 
There is no reason at all why a tncs earthing system cant be used for an outbuilding unless the installation includes areas where tncs restrictions apply,ie construction sites,swimming pools temporary installations exhibition stands etc.
 
Hi.

A PME system can be exported provided that the either of the following 2 conditions are met

1. There are no extraneous conductive parts within the outbuilding i.e steel frame, water service, gas service etc.

2. If there are conductive parts, then the equipotential zone needs to be extended to the outbuilding via main equipotential bonding conductors sized accordingly i.e a minimum of 10mm2 for each service back to the MET within the house, unless the sub-main is greater than 10mm2 itself.


Personally if there are conductive parts within the outbuilding then I always TT regardless of sub-main size.
 
Thanks for everybodys help.I think i will go with the majority and leave the stake in the van.Out of interest another item of differing opinions would you put an rcbo in the house or rcd unit in garage.Thanks.
 
If its SWA submain, then RCD in the garage.

Saves taking the house out when they cut through the lawn mower or hedge trimmer flex. :D
 

Reply to Pme to feed garage. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
546
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
990
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
921

Similar threads

I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
650
Sounds more positive.
Replies
8
Views
761

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top