Hi guys,

thoughts on this would be appreciated.

I have a 3 phase 100 amp PME supply, feeding 3 domestic dwelling about 80 mts away. Done cable calc and have chosen 50mm 4 core swa using armour to protect cable.
In the 1st dwelling I have 3 phase metal DB feeding 3 sub mains, 1 to 1st & 2nd floor flats and 1 feeding separate dwelling. all have metal clad DB utilising RCBO protection on all circuits.

Should I TT at main DB or is it possible to use the PME system through out.

Any food for thought would be appreciated.

Regards

Mike
 
Welcome to the forum, I take it you have made an error in how you word your options, PME is a network system and you are not permitted to continue this, I assume you mean use the earth provided by the Networs PME by extending the equipotential zone.

Anymore details on the supply swa, what are the install methods and front end fusing, it sounds a tad small for a buried cable at 80m with 100amp fusing?
 
Hi guys,

thoughts on this would be appreciated.

I have a 3 phase 100 amp PME supply, feeding 3 domestic dwelling about 80 mts away. Done cable calc and have chosen 50mm 4 core swa using armour to protect cable.
In the 1st dwelling I have 3 phase metal DB feeding 3 sub mains, 1 to 1st & 2nd floor flats and 1 feeding separate dwelling. all have metal clad DB utilising RCBO protection on all circuits.

Should I TT at main DB or is it possible to use the PME system through out.

Any food for thought would be appreciated.

Regards

Mike

Hi Mike, welcome to the forum. The armour wouldn't be adequate as a bonding conductor...Would you mind sharing your calculations? What type of overcurrent protective device is protecting each distribution circuit?
 
Standard 100 amp DNO pme supply, then to 3 phase 80 amp switch fuse, feeding 50 mm 4 core SWA. To DB 1. 3 63 amp MCB sub mains to 3 to 3 flats each with single phase DB loaded with RCBOs
 
Is the SWA buried or clipped direct? This can have a big bearing on its size hence I queried your front end fusing and methods, before we start advising on earthing etc we need to establish your design is correct to suit. I asked because it rang a few alarm bells if I made a few basic likely assumptions.
 
Standard 100 amp DNO pme supply, then to 3 phase 80 amp switch fuse, feeding 50 mm 4 core SWA. To DB 1. 3 63 amp MCB sub mains to 3 to 3 flats each with single phase DB loaded with RCBOs

yes would be fine as circuit protective conductor but not a bonding conductor due to the resistivity of the steel. Having multiple 60898 circuit breakers in series will not provide discrimination.
 
According to IEE sheet I have on 4 core 50mm armour steel is ok to use as CPC. Main DB has 3 X 63 amp mcb sub mains feeding 3 DB fully loaded with RCBO

It might be ok as a CPC but probably won't be as a main bond. What is the steel CSA of the armour? Off the top of my head it would have to be over at least 90sqmm

Mcbs protecting a submain is very poor design, why aren't you using fuses?
 

Reply to PME to remote domestic dwelling in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
477
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top