I have a small 3 phase motor and decided to do a little power factor calculation. The motor is rated as follows: 0.18KW, delta amps=1.01A, Star amps=0.58A, full load power factor=0.76 and full load efficiency=58%.
Now power factor can be calculated as follows: Power (watts) / root3 x volts x amps x efficiency
For star connection, the PF comes out at 0.86. If the math is done when connected in delta, the PF comes out at 0.44!
To check this is true I displayed the current (using a current proble) and voltage on a scope and the shift between the voltage and the current was indeed big at 4mS on the same phase (bare in mind that 5mS is 90 degrees). 4mS equates to a lagging current of around 72 degrees. The cosine of 72 degrees gives a power factor of 0.3! (These values were recorded when the motor was running un-loaded)
Is this correct or am I doing something wrong. If it is correct it means that running a motor in delta is incredibly inefficient and will almost certainly need some kind of power factor correction.
Note: I just mechanically loaded up the motor and the shift between voltage and current reduced 3mS which give a PF of 0.58 so it just goes to show that a motor on no load has a poorer power factor than a motor on full load.
Now power factor can be calculated as follows: Power (watts) / root3 x volts x amps x efficiency
For star connection, the PF comes out at 0.86. If the math is done when connected in delta, the PF comes out at 0.44!
To check this is true I displayed the current (using a current proble) and voltage on a scope and the shift between the voltage and the current was indeed big at 4mS on the same phase (bare in mind that 5mS is 90 degrees). 4mS equates to a lagging current of around 72 degrees. The cosine of 72 degrees gives a power factor of 0.3! (These values were recorded when the motor was running un-loaded)
Is this correct or am I doing something wrong. If it is correct it means that running a motor in delta is incredibly inefficient and will almost certainly need some kind of power factor correction.
Note: I just mechanically loaded up the motor and the shift between voltage and current reduced 3mS which give a PF of 0.58 so it just goes to show that a motor on no load has a poorer power factor than a motor on full load.