Problems with a particular lighting circuit in a church run in MICC results in the MCB tripping intermittently. All lamps OK, good earth continuity at all light fittings, but only a L+N to E Inslation Resistance value of 2.23 MegOhm.
I've also been told that when switching on other lighting circuits on the same CCU the same MCB has tripped.
I can't seem to replicate the fault and have tightened all terminals and redressed all cables running into a 4 x 3 gridswitch.
When carrying out L to L Insulation Resistance tested between the various circuits on the CCU I have had very low readings (ranging from 0 MegOhm to 0.85 MegOhm). Some of the other circuits are visibly no where near to the lighting circuit in question (i.e. in different locations of the church and running in separate cable runs). By removing the lighting circuit neutral conductor from the neutral rail in the CCU, the values increase to 3.5 MegOhm.
Not experienced enough in MICC cables and possible induced voltages or back voltages?
Finally, another intermittent 'fault' is that when turning on the lighting circuit in question, there is sometimes a 'humming' noise coming from the CCU. When applying forward pressure to the furthest right MCB, the humming ceases.
Can anyone help explain what maybe happening?
I've also been told that when switching on other lighting circuits on the same CCU the same MCB has tripped.
I can't seem to replicate the fault and have tightened all terminals and redressed all cables running into a 4 x 3 gridswitch.
When carrying out L to L Insulation Resistance tested between the various circuits on the CCU I have had very low readings (ranging from 0 MegOhm to 0.85 MegOhm). Some of the other circuits are visibly no where near to the lighting circuit in question (i.e. in different locations of the church and running in separate cable runs). By removing the lighting circuit neutral conductor from the neutral rail in the CCU, the values increase to 3.5 MegOhm.
Not experienced enough in MICC cables and possible induced voltages or back voltages?
Finally, another intermittent 'fault' is that when turning on the lighting circuit in question, there is sometimes a 'humming' noise coming from the CCU. When applying forward pressure to the furthest right MCB, the humming ceases.
Can anyone help explain what maybe happening?